Modbus AB SLC500 with PROSOFT slow
Communications systems and equipment. topic
Posted by Mário R Domenici on 19 July, 2002 - 10:33 am
Dear Colleagues:

We have an application running with PLC SLC500 S/03 with PROSOFT MCM 3150 card (working as Modbus
Master RTU module - RS422, 19200Kbaud) it controls an Industrial Computer (IPC - Pentium 266) with 14 scales connected on serial commports (RS422-4 wire connection).

We are handling 350 words (Read) and 62 words (Write) with 6 COMMAND LISTS (4 command list / 2 command list write). We are using FC (function Code) 16 to write and 4 to read registers. Example::

PORT SLAVE FC Start Address Destination Add. CNT
1 1 4 43 0 96
1 1 16 200 110 62

Almost transfer values are floating point (IEEE 754 values).

When we send START COMMAND, PLC/PROSOFT -> IPC
it receives this command in 8 seconds, besides
Scale STARTED immendiatly and SCALE STARTED status be returned in 3 seconds to IPC.

We would like to know if is it possible to improve communication performance?

Also if we connect all devices in RS-485, we will improve speed transaction?

Best Regards,
Mário R Domenici


Posted by Michael E. Crossman on 22 July, 2002 - 3:08 pm
Mario,

You may want to try setting up your write commands as conditional: ProSoft Manual Page 26 -> Conditional commands are executed only when a change in the block of data to be written is detected. Every time the Command List is scanned, the module will compare the data to be written against the data last written. If a change is detected in any value, bit or word, the entire data block controlled by the command is written.

Changing from RS-422 to RS-485 will not help increase speed.

Best regards,
Michael E. Crossman
PLCs Plus International, Inc.
http://www.bkppi.com

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
So, what's with this guy Gideon, anyway? And why can't he ever
remember his Bible?
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive