S5 COMTEXT

M

Thread Starter

Michael

Please Help!
I am trying to get an Siemens op panel (OP5)
to communicate with an Siemens S5100UCPU103 plc.
I am useing COMTEXT ver.3.10
However i get the message: no.115 PC-restart
running!

When i load the standard FB 51 into the PLC
program(S5TD01ST.s5d i get the message: preheader
missing
The above FB51 is for CPU103.
Maybe the file is wrong?
Is it possible to download it from somewhere?
All the parts are items that have been found secondhand.
 
G

Gabriele Corrieri

Hi Michael,
contact me freely, I can send you a Winzip archive with all FB for OP under S5, but I haven't used than I don't help you in troubleshooting.

Gabriele Corrieri
mailto:[email protected]
 
A

Andrew Hawdon

Hi

You also need to add some code to make the comms work. This is documented in the manuals. I have working configurations which I can send if you are still having problems.

Andrew hawdon
 
Michael: Try this
1.- Verify the length of DB51.
2.- Turn on bit on on DB 51 in OB21/22(restart)
3.- Check cable for AS-511.

Regards

Omar Glz.
 