Redundancy in Wonderware
Human-Machine Interface and SCADA. topic
Posted by exabb on 17 March, 2003 - 2:59 am
i would like to know if Wonderware V.7 support also for redundancy? i have 4 client workstation, active & backup server, which all use redundant TCP/IP, is Wonderware V.7 available for those configuration?? please advise


Posted by Yosef Feigenbaum on 17 March, 2003 - 9:55 am
Wonderware V 7.x has a mechanism for implementing backup. The mechanism has to be implemented in scripts.

The all stations connected to the runtime server monitor the runtime server by reading a continually changing tag (ie. Seconds). When the tag stops changing the stations change the node name field in the access names read from the failed server.

BTW, make sure that all tags read from the server exists in the server database.

Good luck,

(8{)} ( .)

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.