Compliance with EN-954-1 Category 3
PLCs and related questions. topic
Posted by Adel Abdellatif on 17 June, 2003 - 1:54 pm
How can one acheive compliance with EN-954-1 category 3, without using a safety module in the PLC? Is there is any other way to acheive such compliance for connecting Emergency stop, and critical signals to a PLC system?

regards
adel


Posted by Daniel Chartier on 19 June, 2003 - 4:47 pm
Hello Adel;

Of course there are ways to achieve compliance to cat 3, even cat 4, without safety PLCs. Cat 3 basically means that a single failure of the control element shall not impede the safety funcvtion of that element (therefore 1oo2 technology) and that the single fault should be detected within a single safety function cycle (therefore monitoring of the safety cycle). Safety relays (such as Pilz and others manufacture)are a common electromechanical technology used to achieve compliance.

Follow the following link to HVGB's pdf on "Safety-related control Systems in accoedance with EN 954-1". It is a precious ressource.

http://www.hvbg.de/d/bia/pub/rep/rep02/bia0697e.htm

Hope this helps,
Daniel Chartier


Posted by BobB on 19 June, 2003 - 5:00 pm
Use an external safety relay that disconnects the power to the PLC output lines.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Shaw's Principle:
Build a system that even a fool can use, and only a fool will
want to use it.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive