Does the ABB AC800M CPU redundancy?
W Weifeng Cao Aug 19, 2004 #4 Of course! AC800M CPU is redundant, the control network interface is also redundant.
J JCC Aug 27, 2004 #6 I would like to know if the ABB AC800M controller can be configured as a slave when talking serially via Modbus protocol to the other DCS device. I appreciate your help on this subject. Regards, JC
I would like to know if the ABB AC800M controller can be configured as a slave when talking serially via Modbus protocol to the other DCS device. I appreciate your help on this subject. Regards, JC
R Rohith Naag Nov 4, 2006 #7 Yes certainly.. there are 5 proceossor modules in AC800M. PM851/856/860/861A and 864A. Out of these 5 the last two i.e PM861A and PM864A has got CPU redundancy..
Yes certainly.. there are 5 proceossor modules in AC800M. PM851/856/860/861A and 864A. Out of these 5 the last two i.e PM861A and PM864A has got CPU redundancy..
B Benlahrech Dec 13, 2007 #8 If you have experience with AC800M system configuration, programming be free to exchange ideas, my email is djamal_1510 @ hotmail. com
If you have experience with AC800M system configuration, programming be free to exchange ideas, my email is djamal_1510 @ hotmail. com