what is the basic differences between contactor and relay and why can't we use the contactor instead of relay and vice versa?
![]() ![]() |
Simply, a relay is cheaper than a contactor - generally. A contactor is used for a higher load. For example, we have pump control applications where the electronics control a relay and the relay controls the contactor which starts the pump.
Also - the relay load to the electronics is lighter where the contactor may draw heavy amps and produce a bigger arc potential when it fires.
Thanks,
Bob Hogg
Also - the relay load to the electronics is lighter where the contactor may draw heavy amps and produce a bigger arc potential when it fires.
Thanks,
Bob Hogg
![]() ![]() |
Thanks Mr.Bobb,
its just now my superior asked me this simple question. actually i was not aware of this thing. for me it was both same. so now you helped me to answer his question in a proper way. once again thanks and do upload things like this.
Regards,
Gireesh Gokuldas
its just now my superior asked me this simple question. actually i was not aware of this thing. for me it was both same. so now you helped me to answer his question in a proper way. once again thanks and do upload things like this.
Regards,
Gireesh Gokuldas
![]() ![]() |
Responding to Anonymous' Feb 5, queries... the following discussion applies to only electrically operated devices:
IEEE Definition
Std 100-1992 "Standard Dictionary of Electrical and Electronic Terms" (Std 100-1992) has many definitions for 'Relay'! Conversely, the Standard's only 'Contactor' definition calls it a 'Load-Switch'! The point is that there is no simple definition.
Historical Perspective
In 1905 'relay' and 'contactor' were defined by the AIEE (predecessor of today's IEEE) as follows:
Relay
A device... by which contacts in one circuit are operated by a change in conditions in the same circuit or in one or more associated circuits.
Contactor
A device... for repeatedly establishing and interrupting an electric power circuit.
Now, in response to your "difference" question... the terms are delineated by the power they must carry. Here are definitions presented in Struthers-Dunn "Relay Engineering" manual (ca 1945):
Relay
An electrically controlled device that opens and closes electrical contacts to effect the operation of other devices in the same or another circuit.
Contactor
A magnetically-operated device, for repeatedly establishing and interrupting an electrical power circuit. It is usually applied to devices controlling power above 5kW, whereas the term 'relay' is ordinarily employed below 5kW. The terms are often used interchangeably.
Regards,
Phil Corso, PE {Boca Raton, FL, USA}
[tal-2@webtv.net] (Cepsicon@aol.com)
IEEE Definition
Std 100-1992 "Standard Dictionary of Electrical and Electronic Terms" (Std 100-1992) has many definitions for 'Relay'! Conversely, the Standard's only 'Contactor' definition calls it a 'Load-Switch'! The point is that there is no simple definition.
Historical Perspective
In 1905 'relay' and 'contactor' were defined by the AIEE (predecessor of today's IEEE) as follows:
Relay
A device... by which contacts in one circuit are operated by a change in conditions in the same circuit or in one or more associated circuits.
Contactor
A device... for repeatedly establishing and interrupting an electric power circuit.
Now, in response to your "difference" question... the terms are delineated by the power they must carry. Here are definitions presented in Struthers-Dunn "Relay Engineering" manual (ca 1945):
Relay
An electrically controlled device that opens and closes electrical contacts to effect the operation of other devices in the same or another circuit.
Contactor
A magnetically-operated device, for repeatedly establishing and interrupting an electrical power circuit. It is usually applied to devices controlling power above 5kW, whereas the term 'relay' is ordinarily employed below 5kW. The terms are often used interchangeably.
Regards,
Phil Corso, PE {Boca Raton, FL, USA}
[tal-2@webtv.net] (Cepsicon@aol.com)
![]() ![]() |
Size. Actually, "contactor" is just a trade name for a type of relay used for power switching, and is sometimes referred to as such. Like any other relay, it should be used within its limits with due consideration given to the application specifics such as switching frequency.
--
Steve Myres, PE
Automation Solutions
(480) 813-1145
--
Steve Myres, PE
Automation Solutions
(480) 813-1145
![]() ![]() |
relay is for control logic. Contactor is for outputs. However, relays can also be used for low-load outputs.
EG
EG
![]() ![]() |
![]() ![]() |
Ya You are very right ...Relay is relay and contactor is contactor... I fully agree with you...
![]() ![]() |
Ans:- there is no such a difference between Relya and contactor as I know. So as a conclusion Relay is relay and contactor is contactor. And relay can be contactor and contactor can be relay.
![]() ![]() |
Ans:- there is a difference between relay and contactor. relay is used in control circuit only but contactor is used in both control and power circuit.
a contactor can be relay but a relay cannot be a contactor.
a contactor can be relay but a relay cannot be a contactor.
![]() ![]() |
Ans. contactor is a heavy duty switch whereas the relay is light duty switch
contactor has a hold on contact whereas relay has no such provision
contactor has a hold on contact whereas relay has no such provision
![]() ![]() |
How about the speed of operation? Any difference between the operating time of relay & contactor relay?
![]() ![]() |
As a rule, contactors are a little slower than relays because the armature is more massive. But there will be overlap as there are slow relays and fast contactors. If you don't mind supplying the current, contactors can be made very fast. I've seen some where the actuation was so fast and positive it sounded like someone smacked the panel with a hammer.
And there are even ballistic contactors made to actuate so quickly that they make contact before the HV they switch has a chance to ionize the air and arc. So it's hard to generalize. Smaller will almost always be faster. We used some tiny reed relays on test equipment that were almost as fast as garden variety transistors.
Regards
cww
And there are even ballistic contactors made to actuate so quickly that they make contact before the HV they switch has a chance to ionize the air and arc. So it's hard to generalize. Smaller will almost always be faster. We used some tiny reed relays on test equipment that were almost as fast as garden variety transistors.
Regards
cww
![]() ![]() |
I think you are all mistaken, We have a contactor relay which is used in switchgears, a Relay used in control systems.
![]() ![]() |
>contactor has a hold on contact whereas relay has no such provision <
Hold on contact is something that can be applied to either component. If anything, it would more apply to the relay than the contactor because the hold is a smaller voltage to keep the coil engaged than what a contactor passes through. Once the coil is closed, one of the normally open circuits will close as well passing a constant power to the coil keeping it energized.
Hold on contact is something that can be applied to either component. If anything, it would more apply to the relay than the contactor because the hold is a smaller voltage to keep the coil engaged than what a contactor passes through. Once the coil is closed, one of the normally open circuits will close as well passing a constant power to the coil keeping it energized.
![]() ![]() |
>Ans. contactor is a heavy duty switch whereas the relay is light duty switch <
>contactor has a hold on contact whereas relay has no such provision <
Sorry Sir, but it's not convincing answer. There are several relay which have 4 contacts, 2NO and 2 NC, example Omron MY4N. If we are using only one NO contact then, we can use the other one as latching/holding contact.
>contactor has a hold on contact whereas relay has no such provision <
Sorry Sir, but it's not convincing answer. There are several relay which have 4 contacts, 2NO and 2 NC, example Omron MY4N. If we are using only one NO contact then, we can use the other one as latching/holding contact.
![]() ![]() |
Contactors have non-hinged armatures, typically double-make or double-break device. They are typically in higher load applications and they typically have less contact bounce and more powerful closing forces than standard relays.
![]() ![]() |
I prefer a more pragmatic definition of Relay vs. Contactor. If, when you energize the device, it goes "click", then it's a relay. If it goes "clunk" then it's a contactor.
;-)
;-)
![]() ![]() |
means "click" little amount of current to energize the coil
means "clunk" a large amount of current drawn by to start the motor..
relay is mostly integrated in PLC controller for controlling a close loop process..
while MC or TC is typically used for a large motor to start with a large amount of current...
means "clunk" a large amount of current drawn by to start the motor..
relay is mostly integrated in PLC controller for controlling a close loop process..
while MC or TC is typically used for a large motor to start with a large amount of current...
![]() ![]() |
Lots of ways of looking at this. Yes, in general, the relay is lighter duty. A light duty relay might be used for current isolation or providing a signal to some kind of monitoring software whilst the contactor would be heavier duty and provide power to a device with more current capability.
The contactor is usually built to be repairable. You can change out the coil for different voltages or flip the contacts to be NO or NC and have at least four sets of contacts (three phases and holding contacts) with the option of adding more to the same armature. If there were an overload added to interrupt current to the coil, it would be referred to as a "motor starter."
The contactor is usually built to be repairable. You can change out the coil for different voltages or flip the contacts to be NO or NC and have at least four sets of contacts (three phases and holding contacts) with the option of adding more to the same armature. If there were an overload added to interrupt current to the coil, it would be referred to as a "motor starter."
![]() ![]() |
Although a Relay is generally non-repairable, you can, however, have different coil voltages and multiple contact options
![]() ![]() |
Are contactors not rated to break faults, whereas relays do not generally have this capability?
![]() ![]() |
A relay is use to switch on/off low power devices. A contactor use to switch on/off high power devices.
![]() ![]() |
The differences:
A Relay:
1. Goes Click when energized.
2. Switches loads of lower wattage
3. Applications include control circuitry
4. Generally switch currents less than 10-15 Amperes.
5. Generally switch voltages less than 240 VAC
6. Switch AC or DC
7. Not normally rated in horsepower.
8. Double throw is typical (normally open and normally closed contacts in one unit).
9. Relay coils are AC or DC, but tend to be 5-24VDC with back emf power diodes to protect relay control electronics.
10. The buck just gets passed here. Relays tend to be "pilot" control devices, controlling more powerful contactors.
A Contactor:
1. Goes Clunk when energized.
2. Switches loads of higher wattage
3. Applications include power circuits (from electric motors to a country's main power grids).
4. Generally switch currents above 10-15 Amperes.
5. Generally switch voltages 120 VAC or greater.
6. Switch AC or DC, resistive or inductive loads, but generally switch AC Loads.
7. Usually includes a horsepower rating.
8. Single throw is the norm (either normally open or normally closed contacts, rarely both).
9. Usually A.C. powered coils (24 VAC for safety- interlocked with EPO or EMO, and Panel open interlock switches; 120-240VAC for simplified operations are typical applications)
10. The buck stops here. Contactors are the real deal. They can be controlled by smaller, less powerful relays.
A Relay:
1. Goes Click when energized.
2. Switches loads of lower wattage
3. Applications include control circuitry
4. Generally switch currents less than 10-15 Amperes.
5. Generally switch voltages less than 240 VAC
6. Switch AC or DC
7. Not normally rated in horsepower.
8. Double throw is typical (normally open and normally closed contacts in one unit).
9. Relay coils are AC or DC, but tend to be 5-24VDC with back emf power diodes to protect relay control electronics.
10. The buck just gets passed here. Relays tend to be "pilot" control devices, controlling more powerful contactors.
A Contactor:
1. Goes Clunk when energized.
2. Switches loads of higher wattage
3. Applications include power circuits (from electric motors to a country's main power grids).
4. Generally switch currents above 10-15 Amperes.
5. Generally switch voltages 120 VAC or greater.
6. Switch AC or DC, resistive or inductive loads, but generally switch AC Loads.
7. Usually includes a horsepower rating.
8. Single throw is the norm (either normally open or normally closed contacts, rarely both).
9. Usually A.C. powered coils (24 VAC for safety- interlocked with EPO or EMO, and Panel open interlock switches; 120-240VAC for simplified operations are typical applications)
10. The buck stops here. Contactors are the real deal. They can be controlled by smaller, less powerful relays.
![]() ![]() |
> what is the basic differences between contactor and relay and why can't we use
> the contactor instead of relay and vice versa?
Basic and main difference is that, contactor have special designed chamber vacuumed or filled with special inert gas, which allow HV to switching but not start ARC!!! Relay don't have this, and when use relay on HV with high current arc flux will occur and this situation will be dangerous. Plus relay is smaller contacts are closer and contact platine are smaller may glue together. Relay are often for current to 10A, contactors may go 25A 63A 150A 300A ...
> the contactor instead of relay and vice versa?
Basic and main difference is that, contactor have special designed chamber vacuumed or filled with special inert gas, which allow HV to switching but not start ARC!!! Relay don't have this, and when use relay on HV with high current arc flux will occur and this situation will be dangerous. Plus relay is smaller contacts are closer and contact platine are smaller may glue together. Relay are often for current to 10A, contactors may go 25A 63A 150A 300A ...
![]() ![]() |
"Basic and main difference is that, contactor have special designed chamber vacuumed or filled with special inert gas, which allow HV to switching but not start ARC!!! "
I have to disagree with the above statement. While a high voltage contactor may have those features, low voltage (<600V) contactors do not typically have those features. Also, there are high voltage, air-break contactors available. Low voltage contactors commonly have arch extinguishing capabilities via arch chutes (air). The basic difference between a relay and a contactors is that contactors typically handle higher currents and in some cases higher voltages, are of sturdy construction, and have application specific features like high interrupting capacity, high withstand ratings, motor service, cyclic service, heavy-duty service, etc.
William (Bill) L. Mostia, Jr. PE
Sr. Consultant
SIS-TECH Solutions, LP
Any information is provided on Caveat Emptor basis.
I have to disagree with the above statement. While a high voltage contactor may have those features, low voltage (<600V) contactors do not typically have those features. Also, there are high voltage, air-break contactors available. Low voltage contactors commonly have arch extinguishing capabilities via arch chutes (air). The basic difference between a relay and a contactors is that contactors typically handle higher currents and in some cases higher voltages, are of sturdy construction, and have application specific features like high interrupting capacity, high withstand ratings, motor service, cyclic service, heavy-duty service, etc.
William (Bill) L. Mostia, Jr. PE
Sr. Consultant
SIS-TECH Solutions, LP
Any information is provided on Caveat Emptor basis.
![]() ![]() |
![]() ![]() |
The 15A limit for a relay is not always appropriate as can be seen on this site concerning a relay which it calls:
"FINDER - 66.82.8.230.0000 - RELAY, PANEL, DPDT, 30A, 230VAC "
see http://uk.farnell.com/finder/66-82-230-0000/relay-panel-dpdt-30a-230va c/dp/1329690
The current rating is also not a simple specification because you need to take into account the steady state value as well as the current breaking capability. The graphs for the "Finder" relay in their technical data sheet in the link above cover these considerations very well. I have just installed this relay to control a 3KW hot water cylinder at 220 Volts. It has to switch 13.6 Amperes. I have a timer which turns on this relay. I selected this relay rather than a three phase contactor because it is about a quarter of the price a similar contactor.
"FINDER - 66.82.8.230.0000 - RELAY, PANEL, DPDT, 30A, 230VAC "
see http://uk.farnell.com/finder/66-82-230-0000/relay-panel-dpdt-30a-230va c/dp/1329690
The current rating is also not a simple specification because you need to take into account the steady state value as well as the current breaking capability. The graphs for the "Finder" relay in their technical data sheet in the link above cover these considerations very well. I have just installed this relay to control a 3KW hot water cylinder at 220 Volts. It has to switch 13.6 Amperes. I have a timer which turns on this relay. I selected this relay rather than a three phase contactor because it is about a quarter of the price a similar contactor.
![]() ![]() |
> what is the basic differences between contactor and relay and why can't we use
> the contactor instead of relay and vice versa?
It is my opinion that a contactor is a device that has a 'floating' contact bar that is drawn either away from or towards contacts wheras a relay always has one end of its switch contact mechanism attached to the connection pin/tag. It is nothing to do with current rating as they can be interchanged to a large extent.
> the contactor instead of relay and vice versa?
It is my opinion that a contactor is a device that has a 'floating' contact bar that is drawn either away from or towards contacts wheras a relay always has one end of its switch contact mechanism attached to the connection pin/tag. It is nothing to do with current rating as they can be interchanged to a large extent.
![]() ![]() |
The plug-in relay often does and all form "C" contacts have a common contact end - however, most industrial rated "relays" are similar to contactors with a floating contact bar (see the AB 700 series - they have both types listed under "relay").
There are many sub groups under the title relay - safety relays, definite purpose, magnetic or "reed" relays, and of course latching relays. You cna make some generalizations about typical relays but so many styles have been in use over the years that there is always an exception or two.
Russ
There are many sub groups under the title relay - safety relays, definite purpose, magnetic or "reed" relays, and of course latching relays. You cna make some generalizations about typical relays but so many styles have been in use over the years that there is always an exception or two.
Russ
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.