Posted by amitava sarkar on 21 March, 2005 - 4:17 pm
Please let me know the parameters to be considered for drum level of a power station. Also, the related calculations.
Amitava Sarkar
Posted by E Feng on 3 April, 2005 - 3:08 pm
what are you asking? PID controller parameters, like gain, integal and deritive or three-element control models?
E Feng (Senior Control Engineer, P.Eng. Ph.D)
Posted by adarsh sharma on 30 September, 2005 - 11:29 pm
setting of PID controller parameters like gain, integral & derivative.
Posted by karthikeyan on 3 April, 2005 - 10:59 pm
hai,
to maintain the normal level in the steam drum we are using 3 element control,in that we are taking the measurements of feed water flow drum level,drum press. and steam flow, steam temp.
from that we control the feed water flow by 3 control valves i.e. the final control elements. In that one is continuous but low pass control valve,another two valves are full capacity but only one valve for working next is bypass for emergency.
what information you want in deep?
Posted by GS on 20 October, 2012 - 7:16 am
which electrical motor (induction/step) is used for controlling valve of feedwater? what will be specifications of electric motor for 500MW Thermal power plant?
Posted by Phil Corso on 20 October, 2012 - 1:56 pm
GS... the BFW Pump requirement is non-linear, that is it varies as the square of Boiler pressure.
Example: for a 2,400 psi plant the BFW power required is (ca) 2.5%; a 5,500 psi plant requires (ca) 6.0%!
Regards, Phil Corso