1) Does the star-delta transformer have a tertiary winding?
2) Is the star side of the star-delta transformer earthed?
3) Where do you "see" the current flow to earth you mentioned? Primary? Or secondary?
Regards,
Phil Corso, PE {Boca Raton, FL, USA}
[tal-2@webtv.net] (Cepsicon@aol.com)
1) The transformer LT is on the star-side, and the HT on the delta-side?
2) The star mid-point is earthed?
3) Distance/grid protection (essentially measuring line impedance to the fault location) is being done via PTs and CTs on the LT star-side? Or, are there PTs and CTs on the HT delta-side?
4) Line-break (LB) fault-mode detection (without short-circuit magnitudes) is very difficult. That is because the only current available is that flowing in the faulted conductor. It is especially exacerbated by the increase in fault-resistance in the dry season.
Nevertheless, there is a technique one can use for LB detection, but it will depend on the answers to the assumptions above.
Regards,
Phil Corso, PE {Boca Raton, FL, USA}
[tal-2@webtv.net] (Cepsicon@aol.com)
1) ye LT on star and HT on delta
2)its earthed
3)Ye its mesuring line impedance but by CTs & PTs on secondary side/HT side and also one leg of PTS are grounded as normal
The question which one of my junior asked me that why its not behaving like a ungrounded system means no current flow in to ground if we have ungrounded secondary winding and why we consider the voltage between voltage/sqrt3 (same as of star). I did not have some logical answers for these simple looking questions
Rajan
If there is no intentional short-to-ground, then, all three terminals should measure (ph-ph) / sqrt(3) to ground. However, when one phase is grounded, then the other two "healhy" phases will measure ph-to-ph between each terminal and ground! For a detailed explanation see thread:
http://www.control.com/984504035/index_html
If a simpler explanation is required, please contact me!
Regards,
Phil Corso, PE {Boca Raton, FL, USA}
[tal-2@webtv.net] (Cepsicon@aol.com)
A) Junior's Query About Circuit Behavior.
Neglecting PT's, the three lines are connected to earth through their line-to-earth capacitance. There is also line-to-line capacitance, but it and the subject of ferroresonance will be ignored for purposes of simplifying this discussion! Each PT is connected between it's line and earth. Each measures (ph-ph)/sqrt 3. Current flow thru each PT is its magnetizing or exciting current. For practical purposes
When an earth-fault occurs, the faulted line voltage drops to zero while the voltage of the two healthy lines rise to ph-to-ph voltage in magnitude. This change in the relative magnitude of the three voltages signals a fault condition and corrective action is initiated. Note, current flows are not necessary.
B) Distance Relaying for Earth-Faults.
Although distance relaying enjoys success in earthed systems, such is not the case with many un-earthed systems.
As stated in previous correspondence voltage and current magnitudes essentially establish the "impedance" (I=E/Z) to the fault location.
However, in un-earthed lines the magnitude of current is very small to begin with. Furthermore, wide variation in parameters such as arc-resistance and soil-conditions (earth-return-circuit) exacerbate the problem.
C) Line-Break or Open-Phase Protection.
Distance relaying does not work for this type of fault. Success of these systems should not rely on voltage and current magnitudes, but instead, on their phase displacements.
For example, if a line breaks downstream of the PT, then there isn't a change in voltage. Earth-fault current magnitude will vary based on location of the break, i.e., sending-end (close-in) or receiving-end (far-out!) Nevertheless, protective schemes have been developed to detect such faults!
SNA, I hope this discussion answers your questions. Please be aware that the subject of protective relaying is a science of its own. But, if you have additional questions please contact me.
Regards,
Phil Corso, PE {Boca Raton, FL, USA}
[tal-2@webtv.net] (Cepsicon@aol.com)
there will be no change in voltage between line voltage.
- Temperature, relative humidity sensors pair with wireless network
- Intrinsically safe accelerometer expands line of hazardous area sensors
- Power: Digital converter growth; fuses, harvesting, supplies, transformers, UPS
- Terminal blocks: 125 A, 1,000 V, 15 mm pitch; 100 kA short circuit current rating
- Industrial Ethernet: High density I/O, no-tool RJ45 Ethernet connector, extenders
- RFID: Tag for boxes or polymeric containers, future trends, training
- Enclose, protect: 2 plastic enclosures; device measures heat, airflow
- Control Engineering System Integrators Hall of Fame
- User group meetings: Trade show, conference, motivational seminar, and party, all in one
- Process safety system: Flexible platform designed to increase plant profitability
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Patronize our advertisers!