I am currently involved in a project upgrading a control system on a plant built in the 1970s. Part of the project involves converting panel annunciators (i.e. panel mounted lights indicating running status of a pump motor) over to a modern conventional PLC/DCS.
Originally the relay contacts and lights operated on 110VDC but the new system will be using 24VDC for loop power. The input impedance of the new system is quite high ~4kohm so the loop current through the relay contacts will be ~6mA. The loop power will therefore be decreasing from a small lamp (estimated 1 or 2 Watts at 110VDC) down to 0.15 Watts after the upgrade.
It has been brought our attention there may be a problem get the relay contacts to make a "solid" conductor when the contact closes. The reason for this is the minimum power required to make good electrical contact through any oxide coating or other poor conducting material that may have formed over the years. Unfortunately I don't have the current relay specification to hand at the moment.
I have two questions:
Is this a genuine problem? How many other people have encountered problems when converting circuits with relay contacts from high power down to low power?
I have read the thread "Oxidation of Relay Contacts", which gives some insight, but am wondering if there other personal experiences that are out there. Any help appreciated.
Originally the relay contacts and lights operated on 110VDC but the new system will be using 24VDC for loop power. The input impedance of the new system is quite high ~4kohm so the loop current through the relay contacts will be ~6mA. The loop power will therefore be decreasing from a small lamp (estimated 1 or 2 Watts at 110VDC) down to 0.15 Watts after the upgrade.
It has been brought our attention there may be a problem get the relay contacts to make a "solid" conductor when the contact closes. The reason for this is the minimum power required to make good electrical contact through any oxide coating or other poor conducting material that may have formed over the years. Unfortunately I don't have the current relay specification to hand at the moment.
I have two questions:
Is this a genuine problem? How many other people have encountered problems when converting circuits with relay contacts from high power down to low power?
I have read the thread "Oxidation of Relay Contacts", which gives some insight, but am wondering if there other personal experiences that are out there. Any help appreciated.