Positioner senses the valve opening through a position feedback link connected to valve stem which is its input signal. I/P converter output is its setpoint input. The difference between these two is the error signal based on which the positioner positions the valve to correct position to reduce error to zero. Hence positioner is nothing but a pneumatic feedback controller. Controlled external supply air to positioner provides power to positioner to position a valve. Also positioner is used in a valve when valve operating signal range is different from I/P converter output range.
In recent days software configurable digital positioner are being used in valves which do not require I/P converter and has many features like advanced valve diagnostics, partial stroke testing, remote communication etc.
Without you knowing the concept of Postioner, who selected you in ESSAR? Pls return to your college and study once again and join... I think it would be better for you. MR
Bye.
Nobody knows everything (even if it is basics)
If some body needs to go back to college, if he/she does not know a basic concept, then everybody will be sitting in college
What is really required, is only the attitude,
to learn and keep learning
you are right with your question i learn detail about the positioner usally i use to only calibrate now i know the detail thankyou please do share your knowledge and problem you face during calibration i will love to read it.
Example:
Inputs to positioner
Air supply (feeding of positioner)
Control pneumatic signal: it comes from I/P equipment
Output: pneumatic signal
Numerical example:
Air supply: 35 psi
Control signal: 3-15 psi
Output : 6-30 psi
- Temperature, relative humidity sensors pair with SureCross Wireless Network
- Intrinsically safe accelerometer expands line of hazardous area sensors
- Power: Digital converter growth; fuses, harvesting, supplies, transformers, UPS
- Terminal blocks: 125 A, 1,000 V, 15 mm pitch; 100 kA short circuit current rating
- Enclose, protect: 2 plastic enclosures; device measures heat, airflow
- Control Engineering System Integrators Hall of Fame
- Listen in: Companies continue DCS investments
- New podcast: Planning your DCS migration
- Control platforms: An industry standard perseveres, in many forms
- IMTS: Robots will fight at the manufacturing technology show
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Patronize our advertisers!