Wago Control Module

A

Thread Starter

Amiya Kumar Kar

Please give me a detailed description of 750-312, 750-513, 750-468, 750-600 Wago Control Module. How it works? If we change anything in connection diagram, then what will happen if any module no is changed?

Amiya Kumar Kar
 
R

Robert Dusza

Amiya,

Check the following website, they will have all the info you need.

http://www.wago.com

Bob

Robert J. Dusza, Jr.
Project & Technical Support Manager
(V) 1-860-647-3219
(F) 1-860-647-3150
E-mail - [email protected]
Manchester Water & Sewer Dept.
125 Spring St. P.O. Box 191
Manchester, CT 06045-0191
 
K

Kanbe Kuroda

Following are simple descriptions...

750-312 = MODBUS FieldBus Coupler RS485 150-19200bps
750-513 = 2N.O Relay Outputs Module
750-468 = 4Ch DC0-10V Analog Inputs Module
750-600 = End Module

You can get the detailed information from the following URL.

http://www.wago.com/wagoweb/documentation/index_e.htm

The IO address is defined by the physical Slot Number and Number of Points it's owned. If you change the module with different type, Internal IO Address might be shifted. You had better check the internal address with actual Modules in an application program if you change...
 