Level indicators
Engineering and workplace issues. topic
Posted by mahesh on 18 May, 2007 - 1:10 am
Can you suggest what type of level indicators are good for liquid tanks (cylindrical) with foam on the surface? Foam thickness is about 7". This foam is developed during stripping because of soaps present in our raw material.


Posted by Kris Anderson (Endress+Hauser) on 18 May, 2007 - 10:42 pm
Depending on the foam density and Dielectric properties and fluid properties you could consider two technologies.

For continuous - guided radar and hydrostatic level. Check our website, http://www.endress.com for Levelflex M - FMP40 (guided radar) and Deltapilot S FMB70 (hydrostatic).


Posted by Anonymous on 21 May, 2007 - 11:15 pm
I tried Ultrasonic and RADAR type transmitters but did not work. Another problem in this vertical tank is high agitation. High turbulence on the surface is also hindering accurate level measurements. For some grades of product we make, foam bubbles in the tank would be as big as 16" dia. Defoamer trial failed to remove the foam. Is magnetostrictive transmitters good for this purpose?

Thanks for your suggestions.


Posted by marc sinclair on 22 May, 2007 - 5:38 pm
Hi,

Yes, foam can be a real killer. I recently had problems with an E+H ultrasonic which couldn't deal with even a small amount of foam. They
recommended and we switched to E+H Radar sensors, which aren't much better. The system currently runs perfectly on float switches, at 1% of the price of the 'technology' and they don't need 1.3Gb of software to set up.

Marc


Posted by De Foam Man on 15 July, 2007 - 1:30 pm
Hello, I manufacture products that control and eliminate foam. If the foam is not present, you can get a true reading from the sensors.

Ask the moderators for my e-mail address if you have any questions. JP


Posted by marc sinclair on 15 July, 2007 - 6:56 pm
Hi, We tried all sorts of defoamers, most of them are either pollutants (High COD/BOD), or they are degraded by the bacteria in the process, or they are supplied by companies with dubious enviromental records. Anyway, why spend even more on chemistry, when any float switch will work. I went to see the system last week, the main tank ultrasonic is struggling to be +/- 15% accurate, the two radar sensors had lost their EEPROM settings (again), one of the Dissolved Oxygen probes has stopped working but despite 50cm of thick foam, the float switches were working perfectly.

Marc Sinclair


Posted by Walt Boyes on 22 May, 2007 - 6:02 pm
Aha!

You have found one of the problem children of measurement.

The fact is, you are trying to make a measurement that does not exist.

You want to measure a variable we'll call "what-the-level-would-be-if-there-weren't-any-vortexing-or-turbul ence-or-foa m."

Problem is, that measurement is exceedingly difficult to infer, and inferential measurement is all you have.

Most people, at this point, give up and try either a load cell, or if they really need some sort of "it goes up and it goes down, and sort of resembles a level measurement" they use a nuclear level gauge.

There are some measurements that are currently impossible with state-of-the-art technology.

This is obviously very close to being one.

If you had no agitation, you could make the measurement. Throwing agitation into the equation makes it near impossible.

If you have already tried radar, ultrasonic, and bubbler level (not likely to work because of the air entrainment that causes the foam), and you have an agitator in the tank so no mechanical in-tank measurement is possible, you are stuck with outside the tank measurements, of which there are only
two: weigh the tank and subtract the tare, or use a nuclear gauge and
calibrate out the foam and the agitator's passage.

Of the two, the nuclear gauge is most likely to give you the best results as far as accuracy or precision of measurement (and they are not the same thing) are concerned.

Good luck.

Walt Boyes
Editor in Chief
Control magazine
www.controlglobal.com
blog:Sound OFF!! http://waltboyes.livejournal.com
_________________

Putman Media Inc.
555 W. Pierce Rd. Suite 301
Itasca, IL 60143
630-467-1301 x368
wboyes@putman.net


Posted by Steve on 22 May, 2007 - 6:12 pm
Magnetostrictive transmitters are very accurate but need maintenance cleaning depending on what they are measuring. The HiTECH unit has an accuracy of 1mm.

http://www.hitechtech.com/magneto-strictive.htm

I would also suggest a Klay/HiTECH pressure transducer mounted at the bottom for your application. If what you are measuring is plyable, it will always read pressure at the sensor. IOW, as long as it doesn't harden up on the tranducer, it will measure the pressure. HTH...

http://www.hitechtech.com/pressure.htm


Posted by Robert Scott on 22 May, 2007 - 6:38 pm
Yes, go with a float and magnetostrictive. The float carries a magnet which surrounds the magetostrictive wire. As long as the crud in the tank does not cause the float to hang up on its central guide, this will work fine.

Robert Scott
Real-Time Specialties
Embedded Systems Consulting


Posted by Mahesh on 24 May, 2007 - 12:21 am
Thanks Mr. Robert. Concern with the float and magnetostrictive is that the rubber crumbs in the tank might stick to the float and create nuisance. Our agitator shaft will always have at least 2" thick rubber. We do hydroblasting once in 2 months to get rid of it.

In this vertical closed tank, we have rubber (density- 790kg/cu.m) and organic solvent. This is stripped with steam from the bottom to coagulate rubber. This process also washes off the soap from the rubber, which causes lot of foam. Agitation makes the rubber to stick on the walls and the shaft. My concern is that rubber might stick to the float also. Appreciate your comments/suggestions.


Posted by Walt Boyes on 24 May, 2007 - 12:49 am
Except that he clearly stated that there is an agitator in the tank. Once around and your transmitter is done.

Walt Boyes
Editor in Chief
Control magazine
www.controlglobal.com
blog:Sound OFF!! http://waltboyes.livejournal.com
_________________

Putman Media Inc.
555 W. Pierce Rd. Suite 301
Itasca, IL 60143
630-467-1301 x368
wboyes@putman.net


Posted by Mahesh on 24 May, 2007 - 12:25 am
Mr Kris,

What do you think about point level radiometric devices for this type of applications? Initially I considered Magnetostrictive but, the rubber crumbs in the tank will stick to the float and might corrupt the device. Appreciate your comments.


Posted by Larry K. on 25 May, 2007 - 10:40 pm
Radiometric would be fine... assuming you do not want to measure the level of foam. Having worked with radiometric devices for many years, they would be a good choice. They are not inexpensive however.

Any manufacturer of these devices would need to know vessel diameter, materials of construction, and vessel wall thicknesses. Does the vessel have a jacket? If so, what is in the jacket?

Larry K.


Posted by Anonymous on 29 May, 2007 - 6:27 pm
Thank you for your suggestion. Yeah these tanks are water jacketed. material is SS 304.

What type of level transmitters do you suggest for level measurement in water pits. My point here is inexpensive and efficient level transmitters. This cuboidal concrete pit contains storm water which is about 10' deep, 6feet length and 5' width. Appreciate your suggestions.

Thank you


Posted by Walt Boyes on 31 May, 2007 - 1:58 am
Depending on the solids and grease content in the stormwater, you can use anything from a float to an ultrasonic level transmitter. Flowline makes a good inexpensive ultrasonic, as do several other manufacturers, including Siemens (Milltronics), Endress+Hauser, Emerson (from their Mowbray line), and MANY others. As David Spitzer and I have found when we produce our "Consumers' Guide to Non-Contacting Level Transmitters" there are over 65 manufacturers of ultrasonic level transmitters in the world.

For this application, I'd use an inexpensive ultrasonic, but I admit to some bias.

Walt Boyes
Editor in Chief
Control magazine
www.controlglobal.com
blog:Sound OFF!! http://www.controlglobal.com/soundoff _________________

Putman Media Inc.
555 W. Pierce Rd. Suite 301
Itasca, IL 60143
630-467-1301 x368
wboyes@putman.net


Posted by Larry K on 31 May, 2007 - 11:07 pm
Regarding the jacketed vessels, best for you to contact one of the radiometric manufacturers. Depending on what part of the world you are in, these are some of the manufacturers:

http://www.bertholdtech.com
http://www.ohmartvega.com
http://www.thermo.com
http://www.endress+hauser.com

As for the water pits, sonic level would probably be the best choice if you want continuous level. Capacitance point level for on/off. Probes come in
various lengths so you can have them be at various lengths for multiple points. Many manufacturers exist for these devices. The following are just a few.

http://www.ohmartvega.com
http://www.endress+hauser.com
http://www.drexelbrook.com
https://pia.khe.siemens.com/index.aspx?nr=4916

Best Regards,

Larry K.


Posted by Mahesh on 1 June, 2007 - 11:27 pm
Thanks every one for invaluable suggestions. I will contact E+H.

Thank you.


Posted by Steve on 19 May, 2007 - 12:34 am
I sure can. If this liquid is going to always be the same specific gravity, the cheapest solution would be a Klay/HiTECH pressure transducer mounted on the bottom of the tank. Here is a link to what I am referring to:

http://www.drlevel.com/conventional.htm


Posted by Valentine Sonnier on 19 May, 2007 - 3:01 pm
Foam is a difficult application for any technology. Non-contacting technologies (through air radar and ultrasonic) are preferred where applicable because they do not reqire maintenance and cleaning. The surface of very wet, dense foam provides a reflective target that is required by these technologies. In this instance the device will accurately read the top of the foam. Dryer foam may absorb the return signal causing unreliable performance. A floating target can be used with these technologies to read the liquid surface level. This solution utilizes a float on the liqid surface with a rod extended through the foam and a target plate above. An offset is entered to the level device and the true level is given regardless of the foam type.

TDR radar and continuous capacitance are contacting technologies that mount on the top of the vessel with cables or rods extending to the bottom. The dryer the foam the better the performance of these devices. If the foam characteristics are right some of these devices may be able to read both the foam level and the liqid level. Very wet, dense foams may cause problems with these technologies because they have similar characteristics as the liquid. If this case the device will measure the top of the foam and not be able to detect the interface level. Build-up on the rod or cable can also be a maintenance issue with these technologies. These devices will also have an issue with "loading" on the cable which requires extra support at the mounting location.

Pressure works well in many foam applications but you are measuring hydrostatic pressure and not true level. If the specific gravity on the material remains constant then the pressure indicator will provide reliable level readings. In dirty liquids these devices will require regular cleaning as the lay on the bottom of the vessel. Installation of pressure can be difficult if the tank is aggitatited.

As you can see each technology has its pros and cons. Foam applications are difficult and should not be approached with "one type fits all" solution. My advice is to find a solutions provider that you can trust, has expertise with all of these technologies, employs them, and guarantees results. That is the only way you can be certain you are getting the right solution for your needs.


Posted by Steve on 22 May, 2007 - 6:07 pm
Val,

As long as the dirty liquid is plyable in the liquid, IOW, the dirt bends and flexes in the liquid, the pressure transducer will still work and not need regular cleaning.


Posted by mohsin on 24 May, 2007 - 11:36 pm
How about using non-contacting radar type on LPG bullets or magnetostrictive would be a better choice.


Posted by Steve on 24 May, 2007 - 11:00 pm
Mahesh-

If you mind me asking, what are you currently using for a level measuring device if this is an existing tank application or is this a newly additional tank for you.


Posted by mahesh on 25 May, 2007 - 10:58 pm
We are currently using DP cells. This works well During start up, readings goes erratic. We will have an operator standing and monitoring the level through the sight glass (top of the tank) for four such tanks until the level is adjusted.

Thank you.


Posted by Steve on 12 June, 2007 - 8:58 pm
Hi Mahesh-

This thread is now three weeks old. I was curious if you have selected or picked a new level controls system yet? Let the thread know when you do. I would be curious which system you picked and how it worked.

Thanks-
-Steve


Posted by Bob Hogg on 31 May, 2007 - 10:27 pm
This unit will solve several problems - is rugged and can give you either 4-20 or switch points and has a a visual to boot! If the glass breaks - nothing happens as the unit is magnetically coupled.

Click on the pdf flyer at the bottom of the page. Each unit is custom made to fit.

http://www.almegcontrols.com/magnetic_level_gauge.htm

You could also have a SS tube with the Almeg continuous transducer inside the tube. The fluid intakes would be screened to keep stuff out. They could build a larger I.D. float so there is more space between the float and tube for product build-up.

Like this link but SS - longer and with less vents and a fitting on top.

http://www.almegcontrols.com/deep_well_probe.htm

Bob Hogg


Posted by Rich Wargo on 17 July, 2007 - 12:42 am
Based on my experience with rubber/latex emulsions, the only suggestions I could make would be either flush-mounted diaphram hydrostatic transmitter(s), or weigh cells, with a point detector (ultrasonic) as a rough overfill indicator. Contact type sensors will get gunked up with the material, while most non-contact types can't deal effectively with the foaming over a measurement range. Using an ultrasonic solely for overfill is acceptable, especially if you wash it down periodically.


Posted by Zack Zwitter on 17 July, 2007 - 4:50 pm
Check out a guided wave radar device. Magnetrol makes a good one that I have experience with. I'm sure there are other brands.

The "wave guide" is just a metal rod so it has no moving parts and it is easy to clean. Also, the wave guide does not need to be straight, so it can be bent around agitators, or into the bottom of a cone bottom tank.

I use them in fermenters to see through the foam on top. Changes in impedance generate reflections which are measured to calculate where along the guide the reflection was generated.

Call magnetrol and I'm sure they can send a rep out to test their instrument for your particular application before you buy...

good luck
-Zack Zwitter


Posted by mahesh on 28 August, 2007 - 4:17 pm
Currently, I am working with a service engineer on radiometric level transmitters. I hope proper sizing to zero off foam and the rubber that sticks to the tank wall should provide better results. I can't use any contact type level transmitters as rubber will stick to the rods (at least 3" thick). Appreciate your comments/suggestions.

Thank you.


Posted by Walt Boyes on 29 August, 2007 - 12:09 am
You will likely have to re-zero the detectors every few weeks, as the signal drifts caused by foam and rubber buildup on the vessel inner walls
increases. If the rubber buildup goes to a maximum, and then doesn't increase, you'll only have to re-zero the detector once or so a year, or
after every cleaning.

Walt Boyes
Editor in Chief
Control magazine
www.controlglobal.com
blog:Sound OFF!! http://www.controlglobal.com/soundoff
_________________

Putman Media Inc.
555 W. Pierce Rd. Suite 301
Itasca, IL 60143
630-467-1301 x368
wboyes@putman.net

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
A real patriot is the fellow who gets a parking ticket and rejoices
that the system works.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive