Grounding of Electronic Control system and Power system
Engineering topic
advertisement
Posted by Ash on 23 May, 2007 - 11:39 pm
Dear Friends,

Can any expert of grounding explain in detail that whether the ground/earth for Electrical Power system and Electronic and Control system should be separate or same, and why?

What are the IEC standards related to that issue?

Posted by burrell11 on 25 May, 2007 - 11:24 pm
I always keep them seperate, if you have a high fault current flow through the power earth, the voltage rise could damage electronic equipment. If the load is reactive higher voltage spikes and harmonics can be even more damaging to electronics.

Posted by Bob Peterson on 26 May, 2007 - 5:44 pm
earth is earth. they all connect together at some point.

Posted by kkk on 1 February, 2008 - 12:38 am
What do you mean by separate, two separate pits for safety and logic grounds? I have read somewhere that these should be separate but also connected to a single point, during whole installation.

Where should I connect my -24V DC?

Posted by gh on 1 February, 2008 - 11:05 pm
Hi dear,

What is your control system architecture?
It is likely depend on it!

Posted by kkk on 2 February, 2008 - 9:48 pm
It is honeywell EPKS with 03 controllers and 04 PLC's. All field signals are coming in C/R and terminating in marshalling cabinets. There is also a hardwired panel which receive data from PLC's.

Some workstations and printers etc, you know the usuals of C/R.

For field instrument power supplies, all 24 V DC power supplies have a common (-24 VDC) connected together, and this common is connected to instrumet/logic ground.

kkk

Posted by Sastry MRKS on 11 February, 2008 - 9:44 pm
In Instrumentation, we generally have 2 types of earth pits installed. One pit is called Shield Earth Pit while the other is called Power earth.

While you are designing a big Instrumentation based process control system, we generally have the following equipment.

1. Drives Panels
2. System Cabinets - with PLC/DCS IO cards, RIOs, etc. (Analog IO cards)
3. Power Distribution Panels
4. Digital Panels (Digital IOs)

So we have to separate drive panel grounding as the panel contains heavy noise/harmonics. Secondly, we have to consider ONE redundant shield Earth Pit & ONE redundant Power Earth Pit. This way, we can ensure that even earthing is redundant and this eliminates chances of earth failure.

Power Earth Pit contains earthing from bulk power supplies, Controller Power Supplies, Panel Earthing, Panel Door Earthing, etc.

Shield earth Pit contains earthing from Analog IO shielding cables, Analog signal isolators/safety barriers, etc.

Hope I am right.

Sastry MRKS

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.