Posted by Zafar on 21 July, 2007 - 12:10 pm
I am new in Allen Bradley PLC. i have SLC500 PLC but i don't have its PC interconnecting cable. Please any one help me to make a cable of Allen Bradley to PC interface.
Posted by Bob Peterson on 21 July, 2007 - 4:04 pm
There is a pinout diagram in the manual if you have a 5/03-4-5.
You need an adapter if you have a 5/01-2, or one of the original block style units.
Micrologix units use a proprietary connector so you have to buy the cable from ab.
Posted by Ken Newcomb on 23 July, 2007 - 8:12 pm
Bob is right.
If you have a 9 pin serial on the SLC:
(pinout of 1747-CP3 from AB)
2-3
3-2
5-5
If you have a "phone jack" port:
You have to use a 1747-pic (RS-232 to DH-485 converter)
Ken
Posted by Mike on 5 August, 2007 - 2:47 pm
Hello, similar question.
I need some help on making a programming cable for a plc5/20 (1785-l20b)
I don't know much about this stuff (just things I came across looking for diagrams etc).
Apparently it's db9 to db25 (in appearence), however, I need to know the pin to pin configuration before I proceed.
Could someone shed some light for me?
Thanks,
Posted by Trevor Ousey \(list\) on 5 August, 2007 - 7:08 pm
The serial cable for a PLC5 is still a null modem cable, the PLC5 manuals
available from http://www.ab.com have excellent diagrams.
Posted by Tom Tran on 7 August, 2007 - 1:23 pm
The wiring diagram for this cable is:
PC PLC5
DB9F DB25M
RXD 02-------------02 TXD
GND 05-------------07 GND
TXD 03-------------03 RXD
DTR 04-| |-04 RTS
DSR 06-| |-05 CTS
RTS 07-| |-06 DSR
CTS 08-| |-08 CD
|-20 DTR
Basically, this is the pinout for the 1784-CP10 cable.
Good luck.<br>
tom. tran @ Industran. com
Posted by aan - on 7 August, 2007 - 1:40 pm
The configuration for 1784-CP10 cable (PLC-5 serial port to PC serial port) is:
PC (DB-9) PLC-5 (DB-25)
2 ----------------------------------------- 2
5 ----------------------------------------- 7
3 ----------------------------------------- 3
4 -- -- 4
6 -- -- 5
7 -- -- 6
8 -- -- 8
-- 20
I hope this helps.
Thanks,
Ikhtiander
Posted by Mike on 9 August, 2007 - 7:03 pm
Thanks everyone, I did find the pinout information in the manual listed on Allen Bradley's site. I just had to look harder I guess... and now I have a better understanding of the different cables, etc...
Thanks again,
Mike
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
In 1750 Issac Newton became discouraged when he fell up a flight of
stairs.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive