For example, suppose you had a panel meter that turned on an output if a voltage reading were within limits. If it simply provided you with access to a pair of terminals which connected directly to the contacts, then these would be "voltage free". If however, there were a 24VDC power supply inside the panel meter and one of the terminals output 24VDC when "on", then it wouldn't be "voltage free".
I think you should be able to see the difference. A "voltage free output" simply closes a switch inside a device and you have to feed a voltage into it somewhere in order to get a signal back out. Again, this isn't a term that you would apply to a simple device like a relay; it is something you would use for a complex device that has relays inside it which it uses to signal (or handshake) with another device.
There are several reasons for designing devices this way. One is that this way it can be electrically compatible with a wide range of signals since *you* provide the voltage which is output. The other reason is that it is cheaper that way since the device doesn't have to have a 24VDC power supply inside it just to provide a signal output. Instead, they rely on you to provide that.
This is one of those terms which has come into use as a short hand description for a common configuration. Note as mentioned above that a "voltage free contact" isn't necessarily an actual relay. It could also be a transistor or opto-isolator.
Any help would be appreciated.
If we assume the PLC has sinking inputs, then one wire would go to the PLC input, and the other would go to 24VDC (or whatever the voltage is). When the contact closes at the pump, the PLC input is connected to 24VDC and sees this as "on". When the contact at the pump opens, the PLC input is disconnected from 24VDC and sees this as "off".
If the PLC uses sourcing inputs, then the second wire goes to the I/O card common instead of 24VDC.
open or closed, unless you supply it. And the
whole idea is that you can use it for whatever
you need within it's ratings. It's just like a
standalone relay as far as contacts are concerned.
These are often referred to as "dry contacts" as
well, which is a bit confusing as it is not really
related to "dry switching".
regards,
cww
Hope this helps.
- ABCs of SBCs: Single board computers for embedded control; Lego learning
- Less, more: NEMA cites less confidence; NAM sees more exports of manufactured goods
- Free webinar on Zigbee for embedded systems
- Better together? Ametek, Dresser-Rand, IntervalZero, Rexroth make acquisitions
- You need 2 monitors: This Website will prove it
- Preview: Mitsubishi iQ controls sequence, motion, process, CNC, robotics; has connectivity
- 30 new Rockwell Automation products integrate hardware, software
- Digital manufacturing: Autodesk Inventor shows component interactions
- Software certified by AT&T: Runs on PDAs, cellphones, enables mobile applications
- Research: HMI supervisory software use increases with service needs
Patronize our advertisers!