Voltage free contact
Information resources, documentation. topic
Posted by Andrew on 16 August, 2007 - 11:10 pm
How does a voltage free contact work?


Posted by Anonymous on 19 August, 2007 - 8:52 pm
This means that the relay contact will be free of voltage. There is no voltage will be there in the relay contacts. So you can switch to any system without any fear.

Best of luck.


Posted by Anonymous on 20 August, 2007 - 12:10 pm
What would be possible application of such contact? I know contacts are mainly used to break circuits. Does voltage free mean that no voltage is present on contact when it is open (no voltage at all)?


Posted by Michael Griffin on 20 August, 2007 - 11:37 pm
It's just a relay contact or opto-isolator or transistor. You need to supply your own signal voltage. The voltage that is present is whatever you supply.


Posted by Anonymous on 21 August, 2007 - 4:44 pm
Hmm, if I understand you correctly, 90% of all contacts are voltage free. For example, if I have standard ordinary relay that has NO and NC contacts, all of them are voltage free, right? Contact that is "no voltage free" has a built in power supply or similar?


Posted by David Adams on 21 August, 2007 - 5:24 pm
Technically, all contacts are voltage free until you connect them to a voltage source. The term "voltage free" means they do not yet have a voltage connected to them so you may provide your own based upon the needs of the machine and/or system involved. They are typically used to isolate two machines, each having it's own voltage source, from one another. That way, machine builder "A" does not care what voltage machine builder "B" uses (one machine may have 24 VDC control power and the other may have 120 VAC control power).


Posted by Michael Griffin on 22 August, 2007 - 10:39 pm
Yes, you could say that an ordinary relay has "voltage free contacts". You wouldn't normally phrase it that way though. The term is normally used for complex devices that have relay (or opto-isolator or transistor) outputs.

For example, suppose you had a panel meter that turned on an output if a voltage reading were within limits. If it simply provided you with access to a pair of terminals which connected directly to the contacts, then these would be "voltage free". If however, there were a 24VDC power supply inside the panel meter and one of the terminals output 24VDC when "on", then it wouldn't be "voltage free".

I think you should be able to see the difference. A "voltage free output" simply closes a switch inside a device and you have to feed a voltage into it somewhere in order to get a signal back out. Again, this isn't a term that you would apply to a simple device like a relay; it is something you would use for a complex device that has relays inside it which it uses to signal (or handshake) with another device.

There are several reasons for designing devices this way. One is that this way it can be electrically compatible with a wide range of signals since *you* provide the voltage which is output. The other reason is that it is cheaper that way since the device doesn't have to have a 24VDC power supply inside it just to provide a signal output. Instead, they rely on you to provide that.

This is one of those terms which has come into use as a short hand description for a common configuration. Note as mentioned above that a "voltage free contact" isn't necessarily an actual relay. It could also be a transistor or opto-isolator.


Posted by dude1977 on 27 March, 2008 - 11:49 pm
If you had a PLC and one of its inputs was connected to a running signal from a pump and the connection was a volt free contact, how would the PLC know that the running signal was high or low? Or would this situation never arise, i.e. would volt free contacts only be used by PLC output cards so that the PLC could generate a signal to maybes to start the pump?

Any help would be appreciated.


Posted by Michael Griffin on 28 March, 2008 - 11:42 pm
In reply to dude1977: A voltage free contact is just a switch. You would need two wires from the PLC to the pump contact.

If we assume the PLC has sinking inputs, then one wire would go to the PLC input, and the other would go to 24VDC (or whatever the voltage is). When the contact closes at the pump, the PLC input is connected to 24VDC and sees this as "on". When the contact at the pump opens, the PLC input is disconnected from 24VDC and sees this as "off".

If the PLC uses sourcing inputs, then the second wire goes to the I/O card common instead of 24VDC.


Posted by Curt Wuollet on 21 August, 2007 - 2:27 pm
It means that there is no voltage on the contacts,
open or closed, unless you supply it. And the
whole idea is that you can use it for whatever
you need within it's ratings. It's just like a
standalone relay as far as contacts are concerned.
These are often referred to as "dry contacts" as
well, which is a bit confusing as it is not really
related to "dry switching".

regards,

cww


Posted by Tom Chubb on 21 August, 2007 - 3:24 pm
It can be used to interface with another machine that has a different voltage to the machine with the relay. For example, you want to give a machine running signal to the other machine, so you energise the relay and use the volt free contacts to tell the other machine that the system is running.

Hope this helps.


Posted by prashant on 22 August, 2007 - 11:45 pm
A voltage free contact provided on a particular contactor does not carry the syatem voltage which basically activates that particular contactor's coil itself. It is free to be used to control another system with different voltage, obviously no contact will be voltage or potential free if it is opearting a control system.

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!