Member Login
Search
Jump to a Date
Sponsored Communities
Cool stuff
Neat Stuff

Visit our shop for nerds in control lifestyle products.
Thermal Overload
The threads that wouldn't die...
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
Fortune
Substitute "damn" every time you're inclined to write "very"; your
editor will delete it and the writing will be just as it should be.
-- Mark Twain
editor will delete it and the writing will be just as it should be.
-- Mark Twain
RSS Feed
www.control.com/rss/
To get a personalized feed, become a member at no cost.
I have been encountering high neutral to earth voltage in the UPS output. Would like to understand the cause and remedy
T.N.Venkatesh
tn.venkatesh@siemens.com
T.N.Venkatesh
tn.venkatesh@siemens.com
What do you mean by high?
What is the ups output supposed to be? US, or some foreign standard voltage?
How far from the UPS is this "jhigh" voltage measured? Is the UPS an SDS?
What is the ups output supposed to be? US, or some foreign standard voltage?
How far from the UPS is this "jhigh" voltage measured? Is the UPS an SDS?
The following things have to be cross-checked.
1. Input and output neutral & earth of UPS is common or not.
2. Whether common input neutral and earth are good. We can find out by checking the same at the input of UPS if input and output earth is common. while checking keep the UPS and load "On".
3. By checking the same you will find the root cause. If neutral is found to be floating then 1:1 isolation transformer has to be put and secondary neutral of transfomer has to be grounded. Note the grounding has to be dedicated.
joydip
jdb_2000 @ rediffmail. com
1. Input and output neutral & earth of UPS is common or not.
2. Whether common input neutral and earth are good. We can find out by checking the same at the input of UPS if input and output earth is common. while checking keep the UPS and load "On".
3. By checking the same you will find the root cause. If neutral is found to be floating then 1:1 isolation transformer has to be put and secondary neutral of transfomer has to be grounded. Note the grounding has to be dedicated.
joydip
jdb_2000 @ rediffmail. com
I am facing the same neutral to earth voltage @3to8 V. Checked earthing & found ok. UPS vendor suggesting to earth UPS output neutral and put in grid earthing . whether this is a correct solution.
Also some times i observed neutral to earth voltage @ 40 - 50 v.
Also some times i observed neutral to earth voltage @ 40 - 50 v.
Hi,
Only sharing my experience.
We had also same experience in our 250kVa UPS. We connect the ground to the neutral of UPS output then problem solved.
This may help you.
Prakash
Only sharing my experience.
We had also same experience in our 250kVa UPS. We connect the ground to the neutral of UPS output then problem solved.
This may help you.
Prakash
I would recommend you check also the live to earth voltage, together with the neutral to earth voltage. If you have a high neutral to earth voltage, and a low live to earth voltage, this means that the output of your UPS is floating, i.e. most probably you have an isolating transformer on the output of the UPS, and there is no connection between the output terminals and the earth. Obviously the difference between the two readings should be you live to neutral voltage.
Whether you want to connect the neutral terminal to earth, or not, depends on the protection systems you have on the output of the UPS. In addition it depends also on how you want to operate your loads (i.e. grounded system or floating system). Before you connect your neutral to earth directly check what earth fault currents the system can tolerate.
Whether you want to connect the neutral terminal to earth, or not, depends on the protection systems you have on the output of the UPS. In addition it depends also on how you want to operate your loads (i.e. grounded system or floating system). Before you connect your neutral to earth directly check what earth fault currents the system can tolerate.
From Control Engineering magazine...
Related articles from Control
Engineering magazine- Motors, drives and motion control: Green Hills Software tapped for Saab UAV
- Rockwell Automation releases VantagePoint for plant data visualization
- Fast HMI application development software
- Control system and instrumentation design software
- Off-line robotics programming software with 3D simulation
- HMIs: Rugged, instrument-grade-glass on projected capacitive touchscreens
- SCADA cyber security lessons from the movie ‘Eagle Eye’
- New keyboard for extreme conditions
Above articles copyright 2008 Reed Business Information.
Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!