1. Orifice plate flow calculation formula is basically based on empirical formulas based on actual testing. Most of the results are available for beta ratio 0.3 to 0.7.
2. Low beta ratio means the plate has a smaller hole i.e pressure loss will be higher. This may cause higher size of pump and more money.
3. Higher beta ratio increases the discharge coefficient uncertainty. Higher beta ratio means low differential pressure across your orifice and some times may be difficult to measure.
4. Higher beta ratio needs longer staright length.
I remember long time back when we used to do manual calculations of orifice plate bore as per BS 1042, we always tried to keep the beta ratio approx. 0.6. Because near to o.6 beta ratio the discharge point curve is almost flat, so that even if there is some mistakes in your manual calculation, overall accuracy is not affected.
Hope this helps a little!
- ABCs of SBCs: Single board computers for embedded control; Lego learning
- Less, more: NEMA cites less confidence; NAM sees more exports of manufactured goods
- Free webinar on Zigbee for embedded systems
- Better together? Ametek, Dresser-Rand, IntervalZero, Rexroth make acquisitions
- You need 2 monitors: This Website will prove it
- Preview: Mitsubishi iQ controls sequence, motion, process, CNC, robotics; has connectivity
- 30 new Rockwell Automation products integrate hardware, software
- Digital manufacturing: Autodesk Inventor shows component interactions
- Software certified by AT&T: Runs on PDAs, cellphones, enables mobile applications
- Research: HMI supervisory software use increases with service needs
Patronize our advertisers!