Here Mr Hart blogs on about his favorite industrial comm protocol.
"In general, the installation practice for HART communicating devices is the same as that for conventional 4-20mA instrumentation. Individually shielded twisted pair cable, either in single pair or multi-pair varieties, is the recommended wiring practice. Unshielded cables may be used for short distances, if ambient noise and cross-talk will not effect communication. The minimum conductor size is 0.51mm diameter (#24 AWG) for cable runs less than 1,524 meters (5,000 ft.) and 0.81mm diameter (#20 AWG) for longer distances"
Given that these are words right from Mr. Hart's mouth, one could conclude that as in most 4-20mA apps, sufficient power supply voltage, truly twisted pair, and shielding are the biggies. (Yes, I know there's no Mr. Hart, but humor me)