You should be more specific. What are you using the fuse for?
Generally the fuse/circuit breaker in wiring is to protect the cable. Sizing of fuses should be done by a competent person with knowledge of the relevant standards.
I think I saw somewhere that there are 3 levels of ignorance:
There are those who don't know, and know that they don't know
-- no problem with these guys.
There are those who don't know, and don't know that they don't know
-- getting scary
There are those who don't know, and think that they do know
-- now THAT's scary.
At least the questions we get are from guys in the first category - it's the ones that don't come up on this or similar forums that are really worrying!
My purpose is to protect the 25 kva transformer. Its ratings are 480V/208V, 3ph, delta star. I need to find proper fuse to protect it, either primary or secondary.
First of all, you have enough information to calculate the current. With the information you provided in the email, the capacity and the volatage rating you can calculate the rated current capacity. You should decide if you wants to protect the transformer from currents over the rated capacity, but consider that the wire you use will also limits your maximum current. this means maybe with a fuse you protect the transformer but the wire could be damaged. You shoul also make a load analisys to determine the current that will be circulating in your circuit.
The guidelines you need are avaialble in the National Electrical Code (NEC) there you can find, methods, restrictions, recommendations and examples.
An excellent magazine/web site is Electrical Construction and Maintenance. They have excellent articles and the magazine in the US is typically free to qualified individuals.
The above two sources I have used frequently. Hope this helps.