Message Time Outs on Data Highway
Communications systems and equipment. topic
Posted by JOSEPHJOEYSHOUSE on 30 October, 2007 - 11:19 pm
We are experiencing message time outs on the data high way. A suggestion was made to speed up the DH+ from 57K to 230K baud. What would be some of the drawbacks of doing this, and what causes message time out faults? How can I resolve this issue? It is a PLC5 that we are dealing with.


Posted by Bradley Hite on 5 November, 2007 - 8:42 pm
Hello,

> We are experiencing message time outs on the data high way. A
> suggestion was made to speed up the DH+ from 57K to 230K baud. What
> would be some of the drawbacks of doing this, and what causes message
> time out faults? <

Message timeouts would most likely be due to communication problems on the DH+ network. Potential causes of these problems could include:
* Bad DH+ cable
* Bad connectors
* EMI or RF interference on DH+ cable
* A malfunctioning DH+ device
* Improper or missing Terminating resistors
* the list goes on.

Increasing the communication speed to 230K will not solve the problem. In fact the problem will more than likely become worse. Furthermore, do all of your DH+ devices even support the higher speed?

> How can I resolve this issue? It is a PLC5 that we are
> dealing with. <

Start looking at the DH+ Diagnostics data on the PLC-5 controllers. If you do not have DH+ diagnostics enabled for the DH+ channels then you
need to enable it.

Physically inspect the DH+ network. Is all of the "blue hose" cable from the same vendor? Are all of the connectors good? Are the correct terminating resistors being used? Etc...

Bradley G. Hite
Intertech Inc
mailto:bhite@myplc.com
Teaching Practical Skills for a Technological World


Posted by Jeremy Pollard on 7 November, 2007 - 3:11 pm
Get an SD card for S&S if you can find one... great diags... I found a rogue 1770-KF2 module with it.

Cheers from: Jeremy Pollard, CET The Caring Canuckian!
www[.]tsuonline.com

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!