Their test program also supports both.
Modbus over (via) TCP has a MBAP header and error check added to the standard Modbus message. In Modbus TCP the station number in the standard message is replaced with the MBAP header and the CRC in the standard message is replaced with the error check. Note that for Modbus via TCP the standard Modbus message can be recoverd by removing the TCP wrapper (MBAP header and error check).
HTH,
Lorne
Modbus over TCP is simply Modbus (RTU or ASCII) ADU embedded in a TCP packet. Port is user assigned. Refer to Modbus specification available on modbus.org.
You are basically going to need a Modbus Serial to Modbus Ethernet protocol converter. There are probably some out there that will do the over TCP to TCP converter but I do not recall ever seeing them. You could use a server that can do envapsulated modbus and modbus Ethernet and bridge the data between the 2.
Kepware has products that can do this.
Fred Loveless
Support Manager
Kepware Technologies
http://www.kepware.com
There are converters available. HMS has several different kinds. For more info:
http://www.anybus.com/support/support.asp?PID=237&ProdType=Any bus%20X-gateway
http://www.anybus.com/support/support.asp?PID=251&ProdType=Any bus%20X-gateway
http://www.anybus.com/support/support.asp?PID=110&ProductType= Anybus%20Communicator
For more info, email:
support@hms.se
/Pat
- Piccolo 32-bit microcontrollers bring real-time control for greater energy efficiency
- Temperature, relative humidity sensors pair with wireless network
- Intrinsically safe accelerometer expands line of hazardous area sensors
- Power: Digital converter growth; fuses, harvesting, supplies, transformers, UPS
- Terminal blocks: 125 A, 1,000 V, 15 mm pitch; 100 kA short circuit current rating
- Enclose, protect: 2 plastic enclosures; device measures heat, airflow
- Control Engineering System Integrators Hall of Fame
- Listen in: Companies continue DCS investments
- New podcast: Planning your DCS migration
- Control platforms: An industry standard perseveres, in many forms
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Patronize our advertisers!