s7 300 cpu change
PLCs and related questions. topic
Posted by jay on 17 November, 2007 - 10:01 pm
Hi,
can anyone please tell me that what the procedure of replacing the cpu of s7 300 plc with s7 400?


Posted by dchartier on 18 November, 2007 - 5:23 pm
Hello;
S7-300 and S7-400 PLCs are very different beasts, in terms of power and physical setup. The form factor of the modules is different (the S7-400 modules being twice as high as their S7-300 equivalents)and the S7-400 modules require the use of a modular backplane (the S7-300 use a support rack and bus connectors).

So if you are asking how to replace physically one S7-300 CPU with a S7-400 CPU, basically it cannot be done.

If however you plan to use the I/O modules of the S7-300 as part of a S7-400 setup, then either the S7-300 CPU can be setup as a Profibus-DP slave, replaced by an IM153-2 slave interface module on Profibus, or data can be exchanged between the 2 CPUs through Ethernet (CP343-1/CP443-1, or Profinet connections). Note that there will be limitations on the amount of data exchanged, S7-300 CPs for example will be hard to connect on slave modules.

Please come back with more preciwe info on what you are trying to do so we can comment with better understanding.

Hope this helps,
Daniel Chartier


Posted by Hartono W on 29 November, 2007 - 1:03 am
Hi,

Hardware:
1. Note the number of DI/DO/AI/AO used in S7-300
2. Get the S7-400 I/O to match the S7-300
3. Configure Hardware accordingly.
Generally, you would not have a problem with CPU memory size as S7-400 has larger capacity.

Software:
1. Check the standard FC/FB used. You might need to reprogram.
2. If SFC/SFB are used, you would need to reprogram.
3. Check the OB used. You might need to reprogram.
4. Rewire IO if required.

Hope this would help.

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!