Member Login
Search
Past & Future Posts
Sponsored Communities
Cool stuff
Neat Stuff

Visit our shop for nerds in control lifestyle products.
Thermal Overload
The threads that wouldn't die...
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
Fortune
Captain Penny's Law:
You can fool all of the people some of the time, and some of
the people all of the time, but you Can't Fool Mom.
You can fool all of the people some of the time, and some of
the people all of the time, but you Can't Fool Mom.
RSS Feed
www.control.com/rss/
To get a personalized feed, become a member at no cost.
we are using 25HP AC induction motor for air compressor.
Due to frequent start/Stop, the contactor kit of starter burnt out frequently.
We want to change the starter to Solid state type.
VFD is the best solution for this but it is very expensive and we don't need so much accuracy in speed.
Can anyone suggest that idea/resources for ssr starter it?
Regards
PRakash
Due to frequent start/Stop, the contactor kit of starter burnt out frequently.
We want to change the starter to Solid state type.
VFD is the best solution for this but it is very expensive and we don't need so much accuracy in speed.
Can anyone suggest that idea/resources for ssr starter it?
Regards
PRakash
It sounds like you need a soft starter. ABB, among others, makes them.
Please define how frequently is the compressor motor cycling on and off.
Modern motor starters will take a fair amount of abuse. If it was me I would look for electrical problems before I start throwing money away on additional hardware.
I would look at loss of phase due to poor voltage regulation during starting. Poor voltage supply can also cause high starting currents. I would monitor/measure inrush current during starting assuming normal running amperage is OK.
Many air compressors have controls that start the motor unloaded. Once the motor is up to speed then the loading solenoid valve permits a load on the motor. This can make a big difference on starting currents and duration. Sometimes the motor is permitted to run continuously and it is loaded or unloaded as needed; this will permit the motor to cool during periods when it is unloaded.
I have never been a fan of definite purpose motor starters in heavy duty applications but they are cheaper for a manufacturer to use. Your air compressor manufacturer may have used one.
A variable frequency drive (VFD) is not needed here. A soft start motor starter works well with high inertia loads and is much more economical. I have used them quite satisfactorily to protect the belts in Reeves variable speed drives for mixer applications.
I hope this helps.
Modern motor starters will take a fair amount of abuse. If it was me I would look for electrical problems before I start throwing money away on additional hardware.
I would look at loss of phase due to poor voltage regulation during starting. Poor voltage supply can also cause high starting currents. I would monitor/measure inrush current during starting assuming normal running amperage is OK.
Many air compressors have controls that start the motor unloaded. Once the motor is up to speed then the loading solenoid valve permits a load on the motor. This can make a big difference on starting currents and duration. Sometimes the motor is permitted to run continuously and it is loaded or unloaded as needed; this will permit the motor to cool during periods when it is unloaded.
I have never been a fan of definite purpose motor starters in heavy duty applications but they are cheaper for a manufacturer to use. Your air compressor manufacturer may have used one.
A variable frequency drive (VFD) is not needed here. A soft start motor starter works well with high inertia loads and is much more economical. I have used them quite satisfactorily to protect the belts in Reeves variable speed drives for mixer applications.
I hope this helps.
Responding to forstand's 20-Nov (19:42) comments:
1) Loss-of-phase would prevent the mmotor from starting.
2) Starting current is not dependent on load, but only motor parameters and supply voltage. I suggest you search the control list archives for a complete discussion on the subject!
3) During the starting phase a motor's impedance is constant, meaning that starting current is directly proportional to voltage!
Regards, Phil Corso (cepsicon@aol.com)
1) Loss-of-phase would prevent the mmotor from starting.
2) Starting current is not dependent on load, but only motor parameters and supply voltage. I suggest you search the control list archives for a complete discussion on the subject!
3) During the starting phase a motor's impedance is constant, meaning that starting current is directly proportional to voltage!
Regards, Phil Corso (cepsicon@aol.com)
Hi,
Thanks for your suggestion.
Here power failure/fluctuation is the major problem. We recorded 120 time power failure per month. With every power failure we required 2 times on and off the machine. I did enquiry on soft starter. This is the best option for this problem.
I want to ask another question:
Can we use this soft starter for Speed control for small application (not required like VFD but slidly like celling fan dimmer)? Can we use Normal 3Phase SSR for motor control for small application up to 1HP, by controlling the gate voltage?
Prakash
Thanks for your suggestion.
Here power failure/fluctuation is the major problem. We recorded 120 time power failure per month. With every power failure we required 2 times on and off the machine. I did enquiry on soft starter. This is the best option for this problem.
I want to ask another question:
Can we use this soft starter for Speed control for small application (not required like VFD but slidly like celling fan dimmer)? Can we use Normal 3Phase SSR for motor control for small application up to 1HP, by controlling the gate voltage?
Prakash
I have had good luck with Allen Bradley SMC Starters http://www.ab.com/industrialcontrols/products/solid-state_motor_contro l/soft_starters/smc-flex.html
From Control Engineering magazine...
Related articles from Control
Engineering magazine- Energy efficiency included in U.S. financial bailout package; NEMA likes it
- Automation and Ethernet Combine for 3D Disney Attraction
- Motor Summit 2008 touts global cooperation on energy efficiency
- PID pump control: Sleep mode saves wear, energy
- Thermometry: Fiber-optic sensor measures temperature to 1,000 °C
- How large is this robot? World's largest, Fanuc says. It is holding...?
- 4 advances in sensors: Keyence, Pepperl + Fuchs, Sick, Turck
- Sustainable manufacturing Website features green machine automation technology
- Controls add to robotic flexibility, application diversity; photo gallery
- ACS Motion Control: Modular system, robotic tuning, stand-alone controller
Above articles copyright 2008 Reed Business Information.
Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!