I'm new to process automation. I have a loop that contains (one butterfly valve + pneumatic actuator + positioner) and (flow meter). I was asked to calibrate the positioner and the valve. The point is that the butterfly valve as far as I could see is not linear. I mean that flow isn't linear with valve position, am I right?? I don't have valve chart so, I'm trying to obtain the curve by some ways. In all cases, I'm asking do I have to teach positioner the curve (input signal 4-20 mA / valve position)?? Or I could rely on PID controller only to handle this non-linearity?
Most likely, if it is a closed loop, your description below is missing the controller. Just hooking a flowmeter straight into the positioner is going to give extremely rough control, if it gives any control at all.
If you will calibrate the "positioner + actuator" portion to stroke the valve from 0% to 100 % with a corresponding 0% to 100% input signal, whether it's 3-15 psi, 4-20ma, or some other standard, then *IF* the PID is properly tuned and the flow transmitter is also properly calibrated, the integral in the controller will bring the valve to the proper position after several reset periods.
Now, if the task is to "calibrate the loop" rather than "calibrate the positioner" then you need to calibrate the positioner+valve assembly, calibrate the flow meter, and calibrate the controller. Then you can tune the controller - but if it is an existing loop that has worked before you can probably just set it up the way it was before and it will probably be pretty close.
Can you shed some light by telling us a little more about the components?
Michael
--
Michael Batchelor
www.IndustrialInformatics.com
To get a characterisation automatically in Excel, you should normalise the flow response numbers (i.e. change them to % of span), then plot the Process Demand against normalised flow and you get the characterisation curve required.
The points of this curve are the points used in the characterisation table inside the positioner or DCS.
The characterisation can be applied to either the PID output as a furmula or look-up table or inside the positioner as a lookup table.
The valve+positioner calibration is usually only the 0 and 100% opening setting (and a 50% check).
I agree that the butterfly valve nonlinearity impacts very negatively in the loop performance. But "flow calibration" is a difficult task. The resulting flow is influenced by several factors:
. Upstream and downstream pressures
. Pipe friction loss
. Other valves losses
. Pumps, etc.
You may use a flowmeter to evaluate the actual relationship between valve opening and flow, and implement a linearization curve. But some of these conditions may change after some time (months, weeks, days, hours�), making your linearization curve give wrong results. The most common problem is positioner calibration drift.
Therefore, and following the KISS principle, I suggest you to try first the PID only, if possible. How many maintenance people (at your site) will understand the linearization, and make a new curve when needed? Think about the long run, and not only immediate performance.
Regards,
Marcos T. Bergamo
The job required was to calibrate the assembly ( valve + actuator + positioner) to make sure that 4mA will give no stem travel and 20 mA will give 100% of stem travel.
I did that but I noticed that between 0 and 100% the relation between input signal and estimated flow by such valve positions was not linear.
These assemblies will work in closed loops with flow meters and PLC with software PID function will take control.
From the beginning I was intending to make a look-up table after PID's output as I thought that this will improve loop performance.
Now, I don't know whether to keep it simple with no curve and let the PID handle this non linearity or to make a look-up table after PID's output.
One more question I have, what are the factors that determine valve's ramp up time and ramp down time?
Once again, I'm really thankful for your replies.
By the ramp time I assume you mean from closed to open with a step change in signal, thats usually a function of the positioner orifice size (assuming it is pneumatic) A typical 6" valve would stroke in less than 5 seconds, much faster than the control loop tuning requires.
I always set my positioner up so that it doesn't start to move before about 4.5 mA that way you can be sure it's closed when the controller is at zero. If the valve is oversized you can also reduce the 20 mA setting to say 60% of full travel that will give a more linear response.
Hope this helps
Roy
On the other hand, if you need to push the performance to its limit for some reason, then it may help to insert some non-linearity into the loop. Hopefully the non-linearity that you insert will just counteract the non-linearity in the control valve, making the total loop linearity better. This can be done in the form of a lookup table that defines a piece-wise linear transformation of the commanded valve position, for example.
One case where I can see the need for such linearization is if the dynamic range of your process variable is very large - like trying to control the flow over a 100 : 1 ratio. In that case tuning the control loop for one end of the range will probably result in unacceptable performance at the other end of the range.
Robert Scott
Real-Time Specialties
- ABCs of SBCs: Single board computers for embedded control; Lego learning
- Less, more: NEMA cites less confidence; NAM sees more exports of manufactured goods
- Free webinar on Zigbee for embedded systems
- Better together? Ametek, Dresser-Rand, IntervalZero, Rexroth make acquisitions
- You need 2 monitors: This Website will prove it
- Preview: Mitsubishi iQ controls sequence, motion, process, CNC, robotics; has connectivity
- 30 new Rockwell Automation products integrate hardware, software
- Software certified by AT&T: Runs on PDAs, cellphones, enables mobile applications
- Research: HMI supervisory software use increases with service needs
- Process modeling: Spreadsheets support multiphase flow simulation
Patronize our advertisers!