I have a ControlLogix with a DHRIO Module. Somebody asked me to program the ControlLogix to send/receive data from a computer through a 1770 KF2. Is this possible? If yes, how can I program it?
Somebody said I don't need to add and configure the DHRIO module to my project in ControlLogix. Instead, when I fill out parameters for MSG instruction, I should select DH+ for the communications. Is it correct?
Can you explain more about "be sure to configure the DHRIO with the slot that the processor is in"?
Thanks a lot.
Billy
I only DHRIO modules into the project if we have Remote IO (RIO) otherwise the IO Led on the ControlLogix will flash. It distracts the shift electricians as there is no IO fault. So with the MSG instruction you just need to create a path manual, check out the DHRIO manual for help. The other way is to place it in the IO tree to start with but delete it after you have done it, the CIP patch will remain in the MSG.
Using RSLinx, browse to the DHRIO module and go to properties (right click the mouse), under one of the tabs you should find a spot where you specify the slot that the processor is. This is only needed if you are using older SLC/PLC hardware or comms to communicate with a ControlLogix. This comes in handy if the HMI/Scada doesn't support the CLX but does PLC5/SLC hardware. Also if you are using the older standard Panelviews this works.
Cheers,
Trevor.
First you make a RS-232 cable for the KF2 to computer that works.
Then you set up the DIP switches on the KF2B to match the computer & DHRIO setup.
Then you make up a short section of Data Highway cable, properly terminated, between KF2 and DHRIO.
Then you choose the appropriate settings for the DHRIO.
Lastly there is a bit of programming on the ControlLogix.
I have a Technical Paper on it.
hugo @ plc-control. com
Just thought I'd mention a USB alternative to the 1770-KF2. Check out the DataLink DL3500-DH+/DF1 http://www.datalinkgateways.com / http://www.datalink.com.mx
Thanks,
Morgan
- Piccolo 32-bit microcontrollers bring real-time control for greater energy efficiency
- Temperature, relative humidity sensors pair with wireless network
- Intrinsically safe accelerometer expands line of hazardous area sensors
- Power: Digital converter growth; fuses, harvesting, supplies, transformers, UPS
- Terminal blocks: 125 A, 1,000 V, 15 mm pitch; 100 kA short circuit current rating
- Enclose, protect: 2 plastic enclosures; device measures heat, airflow
- Control Engineering System Integrators Hall of Fame
- Listen in: Companies continue DCS investments
- New podcast: Planning your DCS migration
- Control platforms: An industry standard perseveres, in many forms
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Patronize our advertisers!