I want to calculate the size of the cable to be used for earthing for 11 kv having a short circuit current as
1) 25KA
2) Above 25KA
Can you e-mail the answer to my question as a table showing the size of earthing cable recommended?
1) 25KA
2) Above 25KA
Can you e-mail the answer to my question as a table showing the size of earthing cable recommended?
Anonymous' 30-Nov (23:28) question needs clarification:
1) What does the 25-kA figure represent... the magnitude of a 3-phase fault, or a single-phase to earth-fault?
2) Is the 11-kV system neutral earthed? If so, is it solidly-earthed? Or is current restricted by installation of a neutral resistor?
3) To properly size a cable, current alone is insufficient! Many of its parameters must be known! What is conductor material: Cu; Al? Constuction type: 3x1/C; 1x3/C? Insulation material? Installation: in air; direct buried; in conduit (magnetic, non-magnetic, plastic, ceramic? Proximity to other cables? Non-sheathed? Magnetic or non-magnetic metal screen?
Please note the above items are only some of the particulars that must be known! And, there are a host of others. Other parameters include, but by no means limited to: ac and dc transients associated with the fault current; clearing time of the protective device, i.e., fuse or breaker!
Regards, Phil Corso (cepsicon@aol.com)
1) What does the 25-kA figure represent... the magnitude of a 3-phase fault, or a single-phase to earth-fault?
2) Is the 11-kV system neutral earthed? If so, is it solidly-earthed? Or is current restricted by installation of a neutral resistor?
3) To properly size a cable, current alone is insufficient! Many of its parameters must be known! What is conductor material: Cu; Al? Constuction type: 3x1/C; 1x3/C? Insulation material? Installation: in air; direct buried; in conduit (magnetic, non-magnetic, plastic, ceramic? Proximity to other cables? Non-sheathed? Magnetic or non-magnetic metal screen?
Please note the above items are only some of the particulars that must be known! And, there are a host of others. Other parameters include, but by no means limited to: ac and dc transients associated with the fault current; clearing time of the protective device, i.e., fuse or breaker!
Regards, Phil Corso (cepsicon@aol.com)
From Control Engineering magazine...
Related articles from Control
Engineering magazine- Rockwell Automation releases VantagePoint for plant data visualization
- Industrial Ethernet advantages using Profinet protocol
- Tips for sustainability in manufacturing
- Deadline extended: Nominate award winning products now for upcoming competition
- Video listen in: Making Coriolis two-wire demands small sacrifices
- Innovative manufacturing companies have a profit advantage over low-price firms
- Fieldbus Foundation Seminar: Chicago
- Radios for long-distance use in industrial mesh network
- Fast HMI application development software
- HMIs: Rugged, instrument-grade-glass on projected capacitive touchscreens
Above articles copyright 2008 Reed Business Information.
Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!