I had made redundancy in ControlLogix on hardware side but facing problem on software side. Primary chasis is synchronized with secondary after any abnormality or you can say switchover is normal.
Tags in the both primary and seconadary topics of RSLinx OPC server are avaliable. But when I check for proper updating of tags in RSLinx OPC server while using RSLinx OPCTest Client, the tag quality is bad and did not update while I toggled in RSLogix5000.
Anyone who can really help me out, plz reply here
or on my personal mail.
thussain @ iael. com
Tags in the both primary and seconadary topics of RSLinx OPC server are avaliable. But when I check for proper updating of tags in RSLinx OPC server while using RSLinx OPCTest Client, the tag quality is bad and did not update while I toggled in RSLogix5000.
Anyone who can really help me out, plz reply here
or on my personal mail.
thussain @ iael. com
Come on Guys help me out..
The probelm is that Tag quality in Rslinx OPC test client is BAD when i implement CLX logix Redundant system, but tag quality is GOOD while using Single CONTROLOGIX system. (mind it that on Hardware primary is sechronized with secondary, switching of chassis is fine )
The probelm is that Tag quality in Rslinx OPC test client is BAD when i implement CLX logix Redundant system, but tag quality is GOOD while using Single CONTROLOGIX system. (mind it that on Hardware primary is sechronized with secondary, switching of chassis is fine )
Talal,
For redundant Controllogix, you need to configure an alias topic.
1. Configure topic for the "primary" controller eg COMPSR_CLX_A.
2. Configure topic for the "secondary" controller eg COMPSR_CLX_B.
3. Configure alias topic COMPSR_CLX that points to both topics defined in step 1 & 2.
Tom Tran
tom.tran@industran.com
For redundant Controllogix, you need to configure an alias topic.
1. Configure topic for the "primary" controller eg COMPSR_CLX_A.
2. Configure topic for the "secondary" controller eg COMPSR_CLX_B.
3. Configure alias topic COMPSR_CLX that points to both topics defined in step 1 & 2.
Tom Tran
tom.tran@industran.com
From Control Engineering magazine...
Related articles from Control
Engineering magazine- Rockwell Automation releases VantagePoint for plant data visualization
- Tips for sustainability in manufacturing
- Deadline extended: Nominate award winning products now for upcoming competition
- Video listen in: Making Coriolis two-wire demands small sacrifices
- Fast HMI application development software
- HMIs: Rugged, instrument-grade-glass on projected capacitive touchscreens
- Third-party remote I/O available for ControlLogix, CompactLogix
- Control system and instrumentation design software
Above articles copyright 2008 Reed Business Information.
Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!