- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
"My shampoo lasts longer than my relationships."
www.control.com/rss
just a quick question - can i use a 4 wire prt instead of a 3 wire one to do the same job? i have a 4 wire prt already and i was trying to interface it with a wheatstone bridge. however i now realise that i need a 3 wire for this. can i use 3 wires off my 4 wire prt and cut one wire off, or will i need to buy a new one?? any feedback much appreciated!!
regards,
jfox
A 4 wire RTD is a 3wire RTD with an extra wire.
1-Accurcay of measurement & Applications.
2-The wiring 3 wire insted of 4 wire.
3-The hard ware " Multiplexer, Transmitter you must change the configuration.
Bryce
What is the function for 3rd wire? It means we can use 2 wire RTD at all. As I said 4 wire provides greater accuracy than the 3wire connection
But it will serve your purpose.
with regards
E.M.V.Prasad
I think that a good practice is join together two wires from one extreme and don't cut the wire, because these wires are normally feeble and very thin. Then it can get broken very easy. Therefore it is like a future spare wire (the 4 wire). I mean the RTD wires are very fragile and can be broken even/including during the connection in the Xmtr or wheatstone bridge. This 4 RTD can work like a 3 RTD but I repeat consider not cutting the wire, keep it, join it together to the same terminal or let loose with insulating tape.
J.Pinzon
Instrument Technician
I have a basic question about connecting a 4 wire RTD to a data logging card. I have a 16 channel HP bench link data logger and a 4 wire (black and red wire) RTD. How do I terminate these 4 wires onto the data logger card???
Thanks,
shiraz
What is the hardware device that you need to connect to? Do you have a link for the manual for the device?
Issac
From here you can download the 34970A User's Guide in pdf:
http://www.home.agilent.com/agilent/techSupport.jspx?pid=100000131 3%3Aepsg%3Apro&pageMode=MN&cc=US&lc=eng
It's really a pleasure to read decent documentation like Agilent's. All sorts of informative data like:
34901A 20-Channel Armature Multiplexer
• 20 channels of 300 V switching
• Connects to the internal multimeter
• For detailed information and a module diagram, see page 164.
Each of the 20 channels switches both HI and LO inputs, thus providing fully isolated inputs to the internal multimeter. The module is divided
into two banks of 10 two-wire channels each.
When making four-wire resistance measurements, channels from Bank A are automatically
paired with channels from Bank B . . . all channels on the module are break-before-make.
34902A 16-Channel Reed Multiplexer module
• Switching speed of up to 250 channels per second
• For detailed information and a module diagram, see page 166.
Use this module for high-speed scanning and high-throughput automated test applications. Each of the 16 channels switches both HI and LO inputs, thus providing fully isolated inputs to the internal multimeter. The module is divided into two banks of eight two-wire channels each.
channels from Bank A are automatically paired with channels from Bank B. You can close multiple channels on this module only if you have
not configured any channels to be part of the scan list. Otherwise, all channels on the module are break-before-make.
page 23 pdf:
wiring connection diagram for 4 wire RTD, for either 34901A or 34902A input module
page 210 pdf:
For 4-wire RTD measurements (FRTD), the instrument automatically pairs channel n with channel n+10 (34901A) or n+8 (34902A) to provide
the source and sense connections.
For example, make the source connections to the HI and LO terminals on channel 2 and the sense
connections to the HI and LO terminals on channel 12. Specify the paired channel in the lower bank (source) as the scan_list channel.
Have fun.
Issac
- Temperature, relative humidity sensors pair with wireless network
- Intrinsically safe accelerometer expands line of hazardous area sensors
- Power: Digital converter growth; fuses, harvesting, supplies, transformers, UPS
- Terminal blocks: 125 A, 1,000 V, 15 mm pitch; 100 kA short circuit current rating
- Enclose, protect: 2 plastic enclosures; device measures heat, airflow
- Control Engineering System Integrators Hall of Fame
- Listen in: Companies continue DCS investments
- New podcast: Planning your DCS migration
- Control platforms: An industry standard perseveres, in many forms
- IMTS: Robots will fight at the manufacturing technology show