Member Login
member
passwd
remember me on
this computer.

- join now -
- forgot username or password? -

Search

Jump to a Date

Sponsored Communities
Cool stuff
Select a topic of interest:
...and press:
Neat Stuff
Control.com Stuff

Visit our shop for nerds in control lifestyle products.

Fortune
Jone's Law:
The man who smiles when things go wrong has thought of someone
to blame it on.
RSS Feed
RSS feed Use this link to get an RSS feed of the Control.com article flow, for private, non-commercial use only:
www.control.com/rss/
To get a personalized feed, become a member at no cost.
Select a Page Style
Select one of the following styles:
- BluFu
- Classic
(cookies required)
advertisement
from the ControlLogix department...
Go online with ControlLogix
PLCs and related questions. topic
Posted by Billy on 8 December, 2007 - 2:54 am
I am programming ControlLogix Ladder Diagrams using RSlogix 5000. I bought a chassis with a Processor only. There are no I/O modules. The processor can talk with my Laptop using serial communication port.

When I go online with ControlLogix processor, I found an interesting issue: I cannot TOGGLE every XIC and OTE. I also cannot FORCE ON every input and output address (both DI and AI). Could any expert tell me what is going on?


Posted by Bob Peterson on 8 December, 2007 - 2:13 pm
I don't know about the forcing, but if there is code in the processor, it is entirely possible that the code is resetting the toggled bit. Using the programming software to trun the bit on or off, does not prevent the plc code from affecting its state.


Posted by Billy on 9 December, 2007 - 5:28 pm
Thanks a lot, Bob,

I am wondering anybody else has more ideas about this?


Posted by Trevor Ousey on 9 December, 2007 - 5:27 pm
Billy, Using TOGGLE does not force or override a bit/bool that is already being set or reset, all it does is toggle the stat of that bit. If you have an OTE and tried to toggle it then quite likely the logic to the OTE is setting/resetting the bit and your TOGGLE does nothing or may change the state for one scan.

FORCES only work on digital IO and not on internal bits, the same as it does for SLC and PLC5's.

And FORCES do not work on Integers/Reals at all, meaning that they will not FORCE Analogue IO. You can do a similar thing with a Integer or Real tag by typing in a relevant value in as the data, but if something else is 'writing' data there then it will be over-written, for example an Analogue input module.

Regards,
Trevor.


Posted by Billy on 11 December, 2007 - 2:23 am
Thanks you so much Trevor. You helped me a lot.

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!