from the analog input department...
Resolution of analog input
Posted by venkatesh on 19 December, 2007 - 10:46 pm
Dear All,
What would be the voltge resolution the PLC can read if the analog input resolution is 16 bit and the input range selected in 0 to 10 volts?
Posted by Curt Wuollet on 19 December, 2007 - 11:32 pm
Approximately 10/16384 unipolar or 20/16384 if bipolar.
cww
Posted by Michael Griffin on 20 December, 2007 - 12:32 am
The resolution would be 10 volts divided by 2 to the 16th power (0.00015 volts).
Posted by Bob Peterson on 20 December, 2007 - 12:30 am
I'll bite.
6535.5 counts per volt.
Posted by Davis Gentry on 21 December, 2007 - 12:59 am
Another student question?
16 bit = 0xffff = 65535 states
0-10 V is a 10 V span
10 V / 65535 states = 1.5259 x 10^-4 V/state
Davis Gentry
Posted by Trevor Ousey on 22 December, 2007 - 2:43 am
David's answer is correct, but you should check with the manual as some modules just use -10 to +10 and then the Most Significant Bit is the signed bit and thereby in reality giving you only a 15 bit resolution. And then some will scale to an over voltage range, i.e. 0 to 10.5v. Cheers.
Posted by Vincent Carpentier on 21 December, 2007 - 1:08 am
The above calculation will give you resolution but you should really look into the absolute accuracy of your measurement.
It is not because you are a resolution of 16-bit that your accuracy is 16-bits. You typically should find the accuracy in the user manual of you devices.
I know that NI Programmable Automation Controller (PAC - http://www.ni.com/pac/) will have that in their user guide.
You can also check out these online ressources:
Understanding Instrument Specifications -- How to Make Sense Out of the Jargon
http://zone.ni.com/devzone/cda/tut/p/id/4439
Meas urement Accuracy of a Data Acquisition Board
http://zone.ni.com/devzone/cda/tut/p/id/4517
Hope this helps,
Vincent Carpentier
Vincent.carpentier - at - ni.com
Quebec and Maritimes Field Sales for National Instruments
Posted by Dobrowolski, Jacek on 3 January, 2008 - 10:13 pm
In case of Siemens S7 IO cards, it is 361.7 uV/bit.
Jacek Dobrowolski
Internet Explorer 6.0 Fix