Unbalanced Load Calculation
Engineering and workplace issues. topic
Posted by Roy Matson on 21 December, 2007 - 12:34 am
I was asked how to calculate the power to a 3 phase delta connected heater if the load is not balanced. We all know the formula W = LV x LA x 1.732 x PF for 3 phase power but I can't remember how to do the same for an un-balanced load. My intuition tells me that using the average current for LA would be close but that seems too simple.

Anyone remember the formula?

Thanks,
Roy


1 out of 1 members thought this post was helpful...
Posted by Phil Corso, PE on 22 December, 2007 - 3:01 am
Responding to Roy Matson's 21-Dec (00:34) question... yes, you are correct. Averaging is not the answer. But first, please clarify your need:

Given the three line currents, Ia, Ib, and Ic, as well as the three line-to-line voltages, Vab, Vbc, and Vca, you want to determine:

1) The heater's total power consumption in Watts?

2) The power consumption of the three heating element?

The answer, like the your previous qustion, can be found in the Control List archives. If a search proves unfruitful, then contact me... on or off list!

Regards, Phil Corso (cepsicon@aol.com)


1 out of 1 members thought this post was helpful...
Posted by Phil Corso, PE on 11 March, 2008 - 12:33 am
Roy, have you resolved the calculation question asked in your 21-Dec-07 (00:34) post?

Phil Corso (cepsicon@aol.com)


Posted by Roy Matson on 12 March, 2008 - 1:18 am
Phil,

Not exactly, I asked several engineer buddies, they couldn't remember either however I concluded that 2 out of 6 elements were toast.

Thanks,
Roy


1 out of 1 members thought this post was helpful...
Posted by Phil Corso, PE on 12 March, 2008 - 10:54 pm
Roy, if you still want the formula, please provide (if available) the three ph-ph voltages, and the three line currents measured before discovering that 2 elements were gone!

Regards, Phil Corso (cepsicon@aol.com)


1 out of 1 members thought this post was helpful...
Posted by Phil Corso, PE on 18 March, 2008 - 12:40 am
Roy, the unsymmetrical loss of elements can be easily explained if the load was wye-connected, with two-paralleled elements per phase.

If the above connection has no neutral wire the remaining resistances are exposed to voltages that could be much higher than expected line-neutral voltage!

Regards, Phil Corso (cepsicon@aol.com)


Posted by Roy Matson on 19 March, 2008 - 12:18 am
Phil,

Yes, even I could calculate a Y configuration but the elements were in delta. When site finally got back to me the phase currents were as follows.

Working element
3.3, 3.3, 3.3

Faulty element
1.9, 1.9, 0

So I concluded there must be 2 elements out. I am still curious as to how to calculate unbalance kW.
It seems from the above results if you subtract the lowest reading 3.3 and calculate that
3.3 x 600 x 1.732 = 3429
then add
1.9 x 600 = 1140, end result 4569 will be correct.
But that's easy, what if all 3 are different?
I thought there would be a simple formula.
It's not that important now, so don't stress over it.

Regards,

Roy


1 out of 1 members thought this post was helpful...
Posted by Phil Corso, PE on 20 March, 2008 - 12:28 am
Roy, it depends on what parameter you have chosen for current!

1) The general formula for a balanced delta-connected resistive-load is:

a) If 3.3A repesents line-current, Ia, then total power is:

Pt = Sqrt(3)(Vab)(Ia).

b) If 3.3A represents phase-current thru an element of the delta-connected load, Iab, then total power is:

Pt = (3)x(Vab)x(Iab).

2) The general formula for an unbalanced delta-
connected resistive load is:

a) If one has access to the individual elements then total power is:

Pt = (Vab)(Iab)+(Vbc)(Ib)+(Vca)(Ic).

b) For the case you cite, it would be helpful to know what parameter the two 1.9A measurements represent!

I apologize for misunderstanding your original question. I thought you wanted to determine the total power for a three-phase load (delta or wye) given the 3 phase-phase voltage magnitudes, |Vab|, |Vbc|, & |Vca|, as well as the 3-line currents magnitudes, |Ia|, |Ib|, & |Ic|.

The above problem requires the use of a mathematical approach known as Symmetrical Components!

Regards, Phil


Posted by Dilip on 31 January, 2011 - 12:24 pm
I work in smelting furnaces, which are basically resistance furnaces. It is a three phase AC system feeding large magnitudes of current (in kiloamperes) to raw material (charge). There is always difference in the current drawn by each phase as well as voltage between them. I want to calculate power consumed what formula should be used.

Another point is whether I should consider load as star or delta for power calculations and how it will be affecting calculations, which one will be more practical? I have a facility to measure voltage between electrode-hearth. But due to unbalance load nature I cannot measure the correct voltage. Any suggestions?


1 out of 1 members thought this post was helpful...
Posted by Phil Corso, PE on 20 March, 2008 - 1:09 am
Roy, I forgot to mention in my earlier post that the 1.9A measurement is indicative of one blown element!

That is, current magnitude, 1.9A, for the damaged case, is 57.7% of the current magnitude, 3.3A, representing the undamaged case. An additional clue is the fact that two of the line-currents are equal, and the 3rd is zero!

Regards, Phil Corso


1 out of 1 members thought this post was helpful...
Posted by Phil Corso, PE on 20 March, 2008 - 10:40 pm

In keeping with one of Control.com's goals, i.e., education of List members (admittedly some acrimoniously), the following Table compares three cases illustrating current distribution and power in a 3-phase, delta-connected system! They are: 1) the balanced case with equal resistive branch-elements; 2) open-circuiting of one branch-element; and 3) open-circuiting of two branch-elements:


---------------------------------------
TABLE A: Per-Unit A & Pwr, D-Load
---------------------------------------
Unit Balanced 1-Res Opn 2-Res Opn
----- -------- --------- ----------
Ia 1.00 1.00 0.00
Ib 1.00 0.58 0.58
Ic 1.00 0.58 0.58
----- -------- --------- ----------
Iab 0.58 0.58 0.00
Ibc 0.58 0.00 0.58
Ica 0.58 0.58 0.00
----- -------- --------- ----------
Pwr 1.00 0.67 0.33
----------------------------------------

The above was derived from the fact that ANY three-phase power problem, configured as wye or delta, balanced or unbalanced, can be represented as a two-loop circuit consisting of just two sources of voltage, and three resistive or complex loads! If additional detail is required, contact me!

Phil Corso (cepsicon@aol.com)



Posted by Son on 6 November, 2008 - 9:11 pm
Unbalanced systems can be evaluated by computing phase current and then apply Kirchoff's law (vector form)
I neutral=-(Ia+Ib+Ic)

First, calculate Ia=Vab/Zab(Zab=R for resister)
similarly calculate Ib=Vbc/Zbc and Ic=Vac/Zbc
Total power dissipated=total I^2*R
(Calculate I using vector form.)

It will be easier to see if we draw 3 phase, delta connected, and then calculate Ia, Ib, Ic separately, also calculate real power for each phase separately and then total it up.

Note: Real current value will be calculated by vector form.

I hope this helps.

Son
www.electrical-designer-guide.com


1 out of 1 members thought this post was helpful...
Posted by Phil Corso on 31 January, 2011 - 3:38 pm
Dilip... the system you describe is somewhat like the classic "unbalanced 3-phase resistive" circuit. However, apparently information in this thread is not quite what you are looking for.

To get idea of the unbalance magnitude you face, please provide:

A) the 3 line-line voltages.

B) the 3 phase-neutral voltages.

C) the 3 line currents.

D) the transformer nameplate data.

Regards, Phil


Posted by L. Burton on 28 September, 2012 - 7:11 pm
We work with resistive heating elements in our products. At times we have unbalanced numbers of heating elements per phase. (i.e., 12 elements divided between three phases)

Could you provide an example calculation of leg current using heater elements arranged 1-1-2 across a three phase delta supply?



1 out of 1 members thought this post was helpful...
Posted by Phil Corso on 29 September, 2012 - 8:55 am
L. Burton... your post is the same as Eric L's in Control.Com Thread http://control.com/thread/1277285012 !

I sent him the general solution covering n-elements/phase arranged as 3-phase, 3-wire delta-load

If you want a copy, contact me at cepsicon@aol.com

Regards, Phil Corso

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2014 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
Computers can figure out all kinds of problems, except the things in
the world that just don't add up.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive