Electrical HV and instrument signal cable segregration
Applications topic
advertisement
Posted by pchan on 16 January, 2008 - 12:27 am
I need to know what is the acceptable distance for segregration of electrical HV voltage cables and instrument signal cables. Both cables are to be run on separate electrical and instrument trays.

Please also code with standards/NEC.

Also, is 24Vdc power supply for field instruments considered as electrical or instrument cables?

Posted by William Galibut on 17 January, 2008 - 12:33 am
So you're letting other engineers do the research for you, eh? I think I can point you in the right direction, but it's up to you to do the research. Check out API RP 552, Section 5.2.6, for the proper segregation of instrument cables from HV cables.

Regarding your 2nd question, in design engineering, power supply cables for instruments are naturally called instrument cables. Why? Because firstly, it is instrument engineering who will be responsible for cable specification and cable routing and termination, etc., not electrical engineering. Secondly, the 24 VDC will be coming from the DCS UPS distribution board, which is still under instrument engineering responsibility. Thirdly, it will be supplying instruments, not electrical equipment.

Posted by Roy Matson on 17 January, 2008 - 12:58 am
Hi,

On a separate tray it should be far enough away, e.g. 9 - 12". It is quite common to use the same tray with a metal barrier for separation. I don't think its the high voltage so much as high current that causes noise by magnetic coupling. Most high voltage cables are armoured and your instrument cable will be shielded so the capacitive coupling is minimal. Noisy loads like VFDs are probably more of a problem. It's important to make sure that your instrument shield is only grounded in one place (usually at control system), otherwise you can get current flow (ground loop) from one part of the plant to another which induces lots of noise. You can't always avoid mixing the cables, but in my experience it is seldom a problem.
The 24Vdc power I would consider as an instrument cable, after all if you get noise in that it will get into all your loops.

Sorry don't know the standards/NEC.

Roy
Instrumentation Consultant

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!