Please also code with standards/NEC.
Also, is 24Vdc power supply for field instruments considered as electrical or instrument cables?
Regarding your 2nd question, in design engineering, power supply cables for instruments are naturally called instrument cables. Why? Because firstly, it is instrument engineering who will be responsible for cable specification and cable routing and termination, etc., not electrical engineering. Secondly, the 24 VDC will be coming from the DCS UPS distribution board, which is still under instrument engineering responsibility. Thirdly, it will be supplying instruments, not electrical equipment.
On a separate tray it should be far enough away, e.g. 9 - 12". It is quite common to use the same tray with a metal barrier for separation. I don't think its the high voltage so much as high current that causes noise by magnetic coupling. Most high voltage cables are armoured and your instrument cable will be shielded so the capacitive coupling is minimal. Noisy loads like VFDs are probably more of a problem. It's important to make sure that your instrument shield is only grounded in one place (usually at control system), otherwise you can get current flow (ground loop) from one part of the plant to another which induces lots of noise. You can't always avoid mixing the cables, but in my experience it is seldom a problem.
The 24Vdc power I would consider as an instrument cable, after all if you get noise in that it will get into all your loops.
Sorry don't know the standards/NEC.
Roy
Instrumentation Consultant
- Temperature, relative humidity sensors pair with SureCross Wireless Network
- Intrinsically safe accelerometer expands line of hazardous area sensors
- Power: Digital converter growth; fuses, harvesting, supplies, transformers, UPS
- Terminal blocks: 125 A, 1,000 V, 15 mm pitch; 100 kA short circuit current rating
- Industrial Ethernet: High density I/O, no-tool RJ45 Ethernet connector, extenders
- RFID: Tag for boxes or polymeric containers, future trends, training
- Enclose, protect: 2 plastic enclosures; device measures heat, airflow
- Control Engineering System Integrators Hall of Fame
- Process safety system: Flexible platform designed to increase plant profitability
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Patronize our advertisers!