Member Login
member
passwd
remember me on
this computer.

- join now -
- forgot username or password? -

Jump to a Date

Sponsored Communities
Cool stuff
Select a topic of interest:
...and press:
Neat Stuff
Control.com Stuff

Visit our shop for nerds in control lifestyle products.

Fortune
Hand, n.:
A singular instrument worn at the end of a human arm and
commonly thrust into somebody's pocket.
-- Ambrose Bierce, "The Devil's Dictionary"
RSS Feed
RSS feed Use this link to get an RSS feed of the Control.com article flow, for private, non-commercial use only:
www.control.com/rss/
To get a personalized feed, become a member at no cost.
Select a Page Style
Select one of the following styles:
- BluFu
- Classic
(cookies required)
advertisement
from the Automation List department...
Voltage induced in multicore cable
Engineering and workplace issues. topic
Posted by sreeraj on 24 January, 2008 - 10:26 pm
I have connected armoured 19 core 1.5 sqmm cable to a 110v ac supply. When one pair is connected to supply even if I keep the other end open, voltage is induced in all wires and the supplied 110v is dropping to 66v ac with respect to ground. We have solved this problem by using twisted multi-pair cables. Why is it happening in multicore?


Posted by Curt Wuollet on 25 January, 2008 - 12:23 am
Because the twisting gives you field cancellation
and the multicore does not?

Regards

cww


Posted by Roy Matson on 26 January, 2008 - 3:27 am
The coupling you see in the 19 core cable is due to the capacitance between the conductors as the nearby wire goes from positive to negative then back again. In the twisted cable each wire runs next to one of the AC wires then the other thus canceling out the effect. Going one step further a grounded screen (shield) is placed between each pair.

Although you see voltage induced in your 19 core if you put your multimeter on AC current you will see very little. In most electrical circuits the induced voltage has little effect because it's shorted out by the load. If you want to see induction at its worst try opening a circuit where there is a coil e.g. solenoid the induced voltage can spike to many times higher that the supply voltage as the coils magnetic field collapses. You will often find Metal Oxide Resistors fitted to a coil to minimize that.

Next time you see those old fashioned bare copper telephone lines look closely, you will find they twist as they go down the road either by moving from one insulator position to another or with jumpers every few poles.

Regards,
Roy


Posted by Amrul on 18 November, 2008 - 11:17 am
I found a similar problem when my 15C cable at 1.8km run has induced at 135V when there are 240V supply injected to another core. I just try to fix the resistor in parallel to relay's coil to absorb the floating voltage since the relay energised at 135V. But how to select the suitable rating for resistor, as I have blown few resistors that I've fixed?

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2009 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2009 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Control Engineering magazine subscription
Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!