I want to connect two masters to one slave
Communications systems and equipment. topic
Posted by jmc on 7 February, 2008 - 11:48 pm
I need two Modbus master hosts to communicate with one Modbus slave.
Current (one master, one slave):
MBMaster1<-->MBSlave
Desired (two master, one slave):
MBMaster1<-->|--------|
|BlackBox|<-->MBSlave
MBMaster2<-->|--------|
De tails:
MBSlave has a RS485 that's converted to RS232
MBMaster1 has a RS232
MBMaster2 has a RS232
MBSlave does not support handshaking/flow-control
MBMaster1 and MBMaster2 are independent, so 'may' send request to MBSlave at random/same time.
Questions:
What do I have to do beforehand for this to work?
What kind of 'black box' solution do I need to buy?
Thank you,
jmczero @ hotmail. com
Posted by Darrin Hansen on 8 February, 2008 - 9:27 pm
Our product, the XLTR-200 serial gateway, has 2 RS485 ports and one RS232 port, each of which can be independently configured as Modbus Master or Modbus Slave ports. It is frequently used to allow 2 master devices to simultaneously access one or more slave devices.
http://iccdesigns.com/Merchant2/merchant.mv?Screen=PRO D&Store_Code=ICC&Product_Code=xltr200
Darrin Hansen
ICC, Inc.
Posted by Ian Milne on 8 February, 2008 - 9:32 pm
Jmc,
One system I am aware of that will fit your needs is the PLC09 Modbus Arbitrator from Calta Computer Systems Limited.
http://www.calta.com/
This unit will allow up to three masters to poll a single Modbus slave.
Ian Milne
Posted by Jerry Miille on 8 February, 2008 - 10:47 pm
The Miille Applied Research Multii-Port is specifically designed for connecting multiple Modbus masters to a network one or more slaves. You can see a data sheet here:
http://www.miille.com/din366-10p.pdf.
Jerry Miille
Posted by CH on 11 February, 2008 - 11:14 pm
Hello...
Check out ProSoft Technology's ProLinx line of products - they've been doing this for years.
Here's a snip directly for the product page:
"The ProLinx Modbus Serial Port Expander module allows you to attach up to three separate Modbus master devices to a single Modbus slave."
Specifically, see: http://www.psft.com/content/view/full/8891
CH
Posted by jmc on 11 February, 2008 - 9:58 pm
Thanks for the info. Are there any that can support up to 115.2k baud? (Not absolutely necessary, but good to know.) Thank you.
Posted by y2khines@gmail.com on 23 April, 2008 - 11:03 pm
Yes. All the new Prolinx units support 115.2 baud.
CH