Member Login
Search
Past & Future Posts
Sponsored Communities
Neat Stuff

Visit our shop for nerds in control lifestyle products.
Cool stuff
Thermal Overload
The threads that wouldn't die...
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
Fortune
job interview, n.:
The excruciating process during which personnel officers
separate the wheat from the chaff -- then hire the chaff.
The excruciating process during which personnel officers
separate the wheat from the chaff -- then hire the chaff.
RSS Feed
www.control.com/rss
from the Transformer Protection department...
Knee Point Voltage of REF CTsIn the protection scheme of 20MVA, 16.5/6.9kV , Delta-Star connected transformer having an impedance of 10 ohms, bushing CTs with ratio of 300/1A are provided for REF Protection. The CTs provided on the line side have an Ith rating of 2000A. The earth fault current of the transformer is limited to 300A approximately using a resistance of 13.3 ohms. (The LV side neutral is earthed)
While calculating the knee point voltage of the CTs for REF protection of the above transformer, should the full fault current of the transformer or merely the earth fault current (300A) be considered?
Regards,
Pramod
While calculating the knee point voltage of the CTs for REF protection of the above transformer, should the full fault current of the transformer or merely the earth fault current (300A) be considered?
Regards,
Pramod
Responding to Pramod's 23-Feb-08 (10:18) query:
1) What is meant by CTs? REF ony requires one CT! Please clarify!
2) Knowledge of the CT kneepoint-voltage is unecessary because the maximum REF current is only 300A.
3) Please explain the "10 Ohm" value... is it the anticipated burden of the REF relay?
4) Knowledge of the kneepoint of the 2000A CTs might be necessary if there are very large motors on the 6.9kV bus!
Regards,
Phil Corso(cepsicon@aol.com)
1) What is meant by CTs? REF ony requires one CT! Please clarify!
2) Knowledge of the CT kneepoint-voltage is unecessary because the maximum REF current is only 300A.
3) Please explain the "10 Ohm" value... is it the anticipated burden of the REF relay?
4) Knowledge of the kneepoint of the 2000A CTs might be necessary if there are very large motors on the 6.9kV bus!
Regards,
Phil Corso(cepsicon@aol.com)
Sir,
1.REF refers to the restricted earth fault protection of the low voltage winding of the transformer in which the ground fault happening only inside the winding of the transformer is detected by placing one current trasformer(CT) on the neutral grounding and three CTs in residual connection on the line side.
2. CTs knee point voltage need to be calculated because, in case of a through fault outside the zone covered by REF CTs, saturation of any one of the CTs on line side may lead to undesired operation of relay.
3.The transformer impedance is 10 percent which I wrongly mentioned as 10 ohms. Sorry for that.
4. The knee point voltage is calculated for 2000A CTs (provided on the line side for differential protection) using the maximum through fault current value.
1.REF refers to the restricted earth fault protection of the low voltage winding of the transformer in which the ground fault happening only inside the winding of the transformer is detected by placing one current trasformer(CT) on the neutral grounding and three CTs in residual connection on the line side.
2. CTs knee point voltage need to be calculated because, in case of a through fault outside the zone covered by REF CTs, saturation of any one of the CTs on line side may lead to undesired operation of relay.
3.The transformer impedance is 10 percent which I wrongly mentioned as 10 ohms. Sorry for that.
4. The knee point voltage is calculated for 2000A CTs (provided on the line side for differential protection) using the maximum through fault current value.
Pramod, the REF you defined is called the partial-differential scheme (earth-faults only) in the USA. It is used for protection of a transformer’s star-connected winding when faster response is required. Following are additional comments:
5) It is more likely found in systems having solidly-earthed neutrals! Thus, earth-fault currents are substantially higher than 300A!
6) Like the typical differential scheme, the area of major concern is unusual CT-ratio mismatch, not CT-saturation. For the parameters you cited, maximum fault-current (neglecting offset and motor contribution) is about 17kA (rms) or about 8 times the CT’s rating. So, if the CT is typical of those used for protection, saturation is not a problem! The reason is that the knee-point is much higher than those used for billing or measurement purposes!
7) Presumably you are not using the secondary line-side CTs asigned to the transformer's differentil protective circuit. Is this correct?
8) Frankly, if the majority of 6.9kV loads
consist of motors or distribution transformers, I would not recommend the REA!
9) BTW, did you mean residual-connection or did you mean parallel-connection of the three line-current CTs?
Regards,
Phil Corso (cepsicon@aol.com)
5) It is more likely found in systems having solidly-earthed neutrals! Thus, earth-fault currents are substantially higher than 300A!
6) Like the typical differential scheme, the area of major concern is unusual CT-ratio mismatch, not CT-saturation. For the parameters you cited, maximum fault-current (neglecting offset and motor contribution) is about 17kA (rms) or about 8 times the CT’s rating. So, if the CT is typical of those used for protection, saturation is not a problem! The reason is that the knee-point is much higher than those used for billing or measurement purposes!
7) Presumably you are not using the secondary line-side CTs asigned to the transformer's differentil protective circuit. Is this correct?
8) Frankly, if the majority of 6.9kV loads
consist of motors or distribution transformers, I would not recommend the REA!
9) BTW, did you mean residual-connection or did you mean parallel-connection of the three line-current CTs?
Regards,
Phil Corso (cepsicon@aol.com)
Pramod, further to my earlier 24-Feb-08 (19:29) response:
10) Hopefully, you realize that since the REF scheme does not respond to earth-faults beyond the protected-zone (star-connected winding), an additional EF relay is required as backup for earth-faults in outgoing 6.9kV feeders!
Regards, Phil Corso (cepsicon@aol.com)
10) Hopefully, you realize that since the REF scheme does not respond to earth-faults beyond the protected-zone (star-connected winding), an additional EF relay is required as backup for earth-faults in outgoing 6.9kV feeders!
Regards, Phil Corso (cepsicon@aol.com)
Sir,
10) Yes, we are providing a differential relay to take care of earth and phase faults from HV side circuit breaker to LV side circuit breaker. In addition an O/C & E/F (51/51N) is also used in the downstream of LV side breaker. Further, a stand by earth fault relay is also provided on the neural of the transformer.
Regards,
Pramod
10) Yes, we are providing a differential relay to take care of earth and phase faults from HV side circuit breaker to LV side circuit breaker. In addition an O/C & E/F (51/51N) is also used in the downstream of LV side breaker. Further, a stand by earth fault relay is also provided on the neural of the transformer.
Regards,
Pramod
Sir,
6) If CTs with ratio of 300/1A were used for REF protection in place of 2000/1A CTs (i.e fault current is approximately 57 times the CT rating in this case), would a knee point check be required even if CT secodaries are arranged in a parallel (residual) connection?
7) Yes, we are using a seperate set of CTs for differential protection.
8) You would not recommend using the REF if the majority of 6.9kV loads consist of motors or distribution transformers. Is that because the starting current of motors & inrush magnetising current of transformers may cause an undesired operation of REF relay.
9) By residual connection, I meant the parallel connection of three line side CT secondaries & one neutral side CT secondary before conneting them to relay.
Regards,
Pramod
6) If CTs with ratio of 300/1A were used for REF protection in place of 2000/1A CTs (i.e fault current is approximately 57 times the CT rating in this case), would a knee point check be required even if CT secodaries are arranged in a parallel (residual) connection?
7) Yes, we are using a seperate set of CTs for differential protection.
8) You would not recommend using the REF if the majority of 6.9kV loads consist of motors or distribution transformers. Is that because the starting current of motors & inrush magnetising current of transformers may cause an undesired operation of REF relay.
9) By residual connection, I meant the parallel connection of three line side CT secondaries & one neutral side CT secondary before conneting them to relay.
Regards,
Pramod
Pramod, re: your 26-Feb-08 (00:27) reply:
Answers 6) & 9), yes!
Answers 7) & 9), thank you for clarification!
11) If you continue with the REA scheme, then keep the 2000/1 CTs. A resistor in series with the EF relay will preclude false operation!
12) Target 10% of EF current (i.e. 10A) as trip set-point.
13) Let me know if you need recommendation for EF protection of 11kV feeders!
Regards, Phil Corso (cepsicon@aol.com)
Answers 6) & 9), yes!
Answers 7) & 9), thank you for clarification!
11) If you continue with the REA scheme, then keep the 2000/1 CTs. A resistor in series with the EF relay will preclude false operation!
12) Target 10% of EF current (i.e. 10A) as trip set-point.
13) Let me know if you need recommendation for EF protection of 11kV feeders!
Regards, Phil Corso (cepsicon@aol.com)
Okay, I have read your clarification,
but I have seen in my plant that REF is not used for distribuition transformer, i.e. 6.6 kv/415 v. What would be reason? Also please clarify, differential protection is also not given in case of distribution transformer. If we connect REF for resistance grounded neutral what would be effect of that?
but I have seen in my plant that REF is not used for distribuition transformer, i.e. 6.6 kv/415 v. What would be reason? Also please clarify, differential protection is also not given in case of distribution transformer. If we connect REF for resistance grounded neutral what would be effect of that?
Responding to Samsung’s 08-May-08 (12:52) query… First, let me point out that this thread started out discussing CT saturation. It morphed into a discussion about REF, but for higher voltage levels than evident in your query.
That said, I’ll address your concerns: first, Restricted Earth Fault relaying, or second, Differential Protection, is never used with the typical LV distribution transformer. Putting safety concerns about neutral-earthing aside, there are several reasons why higher levels of protection are not used:
1) Solidly-earthing the neutral of the secondary wye-winding assures that earth-fault current is high enough, i.e., about the same order of magnitude of a 3-phase or a phase-to-phase fault (please, no trivial arguments that ph-ph is only 87% of 3-ph!) Thus protection for an earth-fault relies on the same devices, i.e., breakers and fuses, installed for that purpose. If the REF method were used then every single distribution circuit, regardless of the protective device used, would require additional sensitive earth-fault detection relaying. The cost would be prohibitive!
2) Differential Protection reduces fault duration. While it can be argued that it provides more sensitive protection for the transformer’s primary winding, its advantage in secondary circuits is limited to situations where it was impossible to coordinate with downstream feeder circuits using only time-current relaying!
3) Protection methods, regardless of sensitivity can’t eliminate electrical faults, but can only reduce their duration, hence diminishing the extent of damage!
4) The single LV distribution transformer, if considered a major economic asset like electrical equipment found at higher voltage levels, would require that alternative distribution schemes be used!
Let me know if additional information is required!
Phil Corso (cepsicon@aol.com)
That said, I’ll address your concerns: first, Restricted Earth Fault relaying, or second, Differential Protection, is never used with the typical LV distribution transformer. Putting safety concerns about neutral-earthing aside, there are several reasons why higher levels of protection are not used:
1) Solidly-earthing the neutral of the secondary wye-winding assures that earth-fault current is high enough, i.e., about the same order of magnitude of a 3-phase or a phase-to-phase fault (please, no trivial arguments that ph-ph is only 87% of 3-ph!) Thus protection for an earth-fault relies on the same devices, i.e., breakers and fuses, installed for that purpose. If the REF method were used then every single distribution circuit, regardless of the protective device used, would require additional sensitive earth-fault detection relaying. The cost would be prohibitive!
2) Differential Protection reduces fault duration. While it can be argued that it provides more sensitive protection for the transformer’s primary winding, its advantage in secondary circuits is limited to situations where it was impossible to coordinate with downstream feeder circuits using only time-current relaying!
3) Protection methods, regardless of sensitivity can’t eliminate electrical faults, but can only reduce their duration, hence diminishing the extent of damage!
4) The single LV distribution transformer, if considered a major economic asset like electrical equipment found at higher voltage levels, would require that alternative distribution schemes be used!
Let me know if additional information is required!
Phil Corso (cepsicon@aol.com)
From Control Engineering magazine...
Related articles from Control Engineering magazine- OPC: Painless migration, classic OPC DA to OPC UA, partership
- Easier: panel designs, short-circuit current rating compliance
- MechatronicsZone road show kicks off
- ODVA, DeviceNet: New CIP specs; ControlNet added; 2009 meeting
- Partnership: Advanced, interoperable motion control, machine tools
- Protect intellectual property: Encrypt firmware, control code
- Embedded, wireless devices, dynamic IP routing
- Portable computing: Operators can be mobile with rugged HMI
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!