Member Login
Search
Jump to a Date
Sponsored Communities
Cool stuff
Twitter Feed
Neat Stuff

Visit our shop for nerds in control lifestyle products.
Thermal Overload
The threads that wouldn't die...
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
Fortune
Chapter 1
The story so far:
In the beginning the Universe was created. This has made a lot
of people very angry and been widely regarded as a bad move.
The story so far:
In the beginning the Universe was created. This has made a lot
of people very angry and been widely regarded as a bad move.
RSS Feed
www.control.com/rss/
To get a personalized feed, become a member at no cost.
Whar is over fluxing & how it is worked? is it very hearmful to a Transformer?
What will be the set value of over fluxing relay of a 2 X 10MW captive power plant, having 2nos of 12.5MVA, 33/11KV transformer and both are running in synchronised condition with grid.
What will be the set value of over fluxing relay of a 2 X 10MW captive power plant, having 2nos of 12.5MVA, 33/11KV transformer and both are running in synchronised condition with grid.
Sarkar, responding to your questions in the order they were asked:
1. Overfluxing of a transformer occurs when its flux density exceeds rated density.
2. It is caused when its V/f ratio is greater than that which the manufacture deems is safe. This, of course, is the case when it is connected directly to the generator, i.e., without benefit of an intervening circuit-breaker, and the generator’s excitation system is energized while accelerating to operating speed!
3. Yes it is harmful. The effect is to produce a disproportionate increase in magnetizing-current and excessive iron-losses.
4. Of course, there are tolerable limits. But, the set-value for the relay should be supplied by the manufacturer!
Regards,
Phil Corso (cepsicon@aol.com)
1. Overfluxing of a transformer occurs when its flux density exceeds rated density.
2. It is caused when its V/f ratio is greater than that which the manufacture deems is safe. This, of course, is the case when it is connected directly to the generator, i.e., without benefit of an intervening circuit-breaker, and the generator’s excitation system is energized while accelerating to operating speed!
3. Yes it is harmful. The effect is to produce a disproportionate increase in magnetizing-current and excessive iron-losses.
4. Of course, there are tolerable limits. But, the set-value for the relay should be supplied by the manufacturer!
Regards,
Phil Corso (cepsicon@aol.com)
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2009 Nerds in Control, LLC. All rights reserved.