Pressure Sensor Output
PLCs topic
advertisement
Posted by Jasir Sabri on 15 March, 2008 - 4:20 pm
I have a pressure sensor giving an output of 1-5 Volts. My PLCs analog module takes an input of 0-10V. It's an 8 bit Module (0-255). The pressure sensor has a measurement range of -760mmHg - +760mmHg. The normal operation of my process is from 0 mmHg to -110 mmHg. In this case, which is better....to change the sensor or to use a high resolution analog module?

Posted by Robert Scott on 15 March, 2008 - 5:56 pm
If -760mmHg to +760mmHg corresponds to +1 to +5 volts, then your working range of 0 to -110 mmHg will produce a span of 0.289 volts. Reading that through an 8-bit A/D converter that is expecting 0 to +10v will transform that 0.289 volt span into a span of only 7 counts. I don't know what resolution you need in your application, but I'll bet it is more than 7 discrete levels.

As for your two solutions, either one will work. But getting a different sensor has the advantage that electrical noise will be easier to manage. You may end up needing to do both - get a different sensor and get a higher-resolution A/D.

Robert Scott
Real-Time Specialties
Embedded Systems Consulting

Posted by Michael Griffin on 16 March, 2008 - 4:05 pm
The conventional answer is to a signal conditioner to change the 1-5 volts to 0-10V. If you are really only using part of the range, you could even expand the signal more so that 0 - 110 mmHG (or whatever is suitable) is 0-10V. You just need to use a signal conditioner that has that much adjustment range. This much adjustment though would require a signal conditioner that has multiple range jumper settings plus potentiometer adjustment for fine tuning.

Posted by Jasir Sabri on 12 April, 2008 - 3:15 am
Thank You Friends for your valuable suggestions.

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!