50 hp motor connectionI have a question.
We have a 50 hp motor running having rated current of 75 amps. This motor winding is connected in star and the starter used is a DOL starter(Direct 0nline). The motor is running at close to rated HP.
My question is if we now connect the motor winding in delta what will happen to
1) starting current
2) running current
3) starting and running torque
4) Will the mechnical load it is driving get affected.
5) Normally which is the configuration in which a motor needs to be connected during running.
Hope i am clear in my in what clarification i seek
We have a 50 hp motor running having rated current of 75 amps. This motor winding is connected in star and the starter used is a DOL starter(Direct 0nline). The motor is running at close to rated HP.
My question is if we now connect the motor winding in delta what will happen to
1) starting current
2) running current
3) starting and running torque
4) Will the mechnical load it is driving get affected.
5) Normally which is the configuration in which a motor needs to be connected during running.
Hope i am clear in my in what clarification i seek
>I have a question.
>We have a 50 hp motor running having
>rated current of 75 amps. This motor
>winding is connected in star and the
>starter used is a DOL starter(Direct
>0nline). The motor is running at close
>to rated HP.
>
>My question is if we now connect the
>motor winding in delta what will happen
>to
>1) starting current <
Will go up considerably
>2) running current <
As above
>3) starting and running torque <
Starting torque will go up but running torque should stay the same for same load
>4) Will the mechnical load it is
>driving get affected. <
Yes the additional starting torque will put extra stress
>5) Normally which is the configuration
>in which a motor needs to be connected
>during running. <
This depends on the voltage you shouldn't connect in delta unless it's designed for it.
Please give the system voltage Phase-phase Nameplate voltage.
Regards
Roy
>We have a 50 hp motor running having
>rated current of 75 amps. This motor
>winding is connected in star and the
>starter used is a DOL starter(Direct
>0nline). The motor is running at close
>to rated HP.
>
>My question is if we now connect the
>motor winding in delta what will happen
>to
>1) starting current <
Will go up considerably
>2) running current <
As above
>3) starting and running torque <
Starting torque will go up but running torque should stay the same for same load
>4) Will the mechnical load it is
>driving get affected. <
Yes the additional starting torque will put extra stress
>5) Normally which is the configuration
>in which a motor needs to be connected
>during running. <
This depends on the voltage you shouldn't connect in delta unless it's designed for it.
Please give the system voltage Phase-phase Nameplate voltage.
Regards
Roy
Dear Thompson,
Starting current in case of delta will increase in this case. You may use an AC current measuring clamp meter to measure it.
Running current in delta configuration, you may easily find on the name plate of the motor. Similarly you may measure it as per actual in running condition.
Torque is related to current.
Mechanical stresses increase with increase in starting current.
Star or delta in running condition may be decided by you depending upon RPM you require during running operation as mentioned on the name plate.
If there are more mechanical stresses leading to frequent break down, then you must use soft starter for your application.
Starting current in case of delta will increase in this case. You may use an AC current measuring clamp meter to measure it.
Running current in delta configuration, you may easily find on the name plate of the motor. Similarly you may measure it as per actual in running condition.
Torque is related to current.
Mechanical stresses increase with increase in starting current.
Star or delta in running condition may be decided by you depending upon RPM you require during running operation as mentioned on the name plate.
If there are more mechanical stresses leading to frequent break down, then you must use soft starter for your application.
From Control Engineering magazine...
Related articles from Control Engineering magazine- OPC: Painless migration, classic OPC DA to OPC UA, partership
- Easier: panel designs, short-circuit current rating compliance
- MechatronicsZone road show kicks off
- ODVA, DeviceNet: New CIP specs; ControlNet added; 2009 meeting
- Partnership: Advanced, interoperable motion control, machine tools
- Protect intellectual property: Encrypt firmware, control code
- Embedded, wireless devices, dynamic IP routing
- Portable computing: Operators can be mobile with rugged HMI
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!