Pump stroke adjustment
Applications topic
advertisement
Posted by Pchan on 3 April, 2008 - 12:11 am
I need to increase/decrease a chemical injection pump stroke adjustment for speed via DCS. I need to know if any pump vendor or anyone has experience in connecting electric actuator on the pump to the DCS (analog output) so that we can increase/decrease the pump stroke adjustment.

If the electric actuator can receive 4-20 ma, do we need to have two analog outputs from DCS for increase/decrease or is one analog output sufficient?

Please offer your advice. Thanks.

Posted by Rob Barrese on 3 April, 2008 - 10:58 pm
To all,

Milton Roy makes adjustable positive displacement pumps suitable for chemical injection. Only one analog output will be required.

http://www.miltonroy.com/corp/details/0,10294,CLI1_DIV39_ETI3654,0 0.html

Milton Roy is not the only game in town, there are many others.

Rob Barrese
ArcelorMittal Dofasco

Posted by cliff on 3 April, 2008 - 11:46 pm
One output is all that is need as it should control the speed of the pump and thus the stroke or at least thats how we control the LMI pumps.

Posted by Roy Matson on 5 April, 2008 - 1:40 am
If your metering pump is one of the smaller variety where the diaphragm is driven by a solenoid, another possibility is to drive it from a pulse train generated by the DCS.

Some of the pumps I work with have provision for a low voltage pulse input, others I have driven the coil directly using an interposing relay. By counting the pulses and multiplying by stroke volume you have a rough idea of the total flow and can calculate rate. This can easily be verified by timing to a graduated cylinder.

Hope you find this useful.

Regards,
Roy

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!