Posted by khizar hayat on 3 April, 2008 - 11:46 pm
I want to know whether it is better to install a DP type level transmitter or torque tube type level transmitter on the slug catcher.

The slug catcher is installed on the natural gas well for removal of any water/slug.

Posted by Roy Matson on 5 April, 2008 - 1:31 am
Khizar,

I'm not sure what a Slug Catcher is, but I assume it's some form of high pressure vessel and the slugs of water will be travelling at high velocity. If this is the case, the Displacer of the torque tube transmitter might be subject to considerable violence (if in the vessel).

In my humble opinion a DP cell is much more likely to last but you also have to consider freezing and other issues.

Regards,
Roy

Posted by khizar hayat on 5 April, 2008 - 5:05 pm
Slug Catcher is a sort of knock out vessel downstream of the gas well for removal of any condensate/slug from the gas.It will be subject to the well head pressure of approximately 40Kg.
DP cell with diaphragm seal can be used.On the other hand torque tube displacer can be mounted in an additional housing with two tappings from the side of the vessel.

Now with this information which solution will be better.

Posted by Roy Matson on 6 April, 2008 - 9:36 pm
Khizar,
While there is nothing wrong with your torque tube I think that type will be expensive.
Personally I try to avoid diaphragm seals with capillary on a transmitter unless it's a 3" Flange mount level. If you can run the LP side dry or perhaps with a seal fluid e.g. oil or glycol it would be cheaper and less likely to fail through damage. I have found for condensing fluids if you run the LP tubing a couple of feet higher and then back down to the tapping point you get very little liquid at the transmitter.

I'm surprised you didn't get more response on this post, there must be lots out there with more experience than I on this issue.

Good Luck
Roy

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!