How the Vector group of step up transformer to be written
Application Questions and Problems topic
Posted by Truong Cong Le on 5 April, 2008 - 4:56 pm
When we say "step up transformer," How the connection group to be defined: Voltage vector of HV 35kV to be taken for reference or Voltage vector LV 0.4kV.

I can not understand what is wrong, what is right:

- some people say: y/D11 is right (1)
- other people say:D/y11 is right (2)

Please be so kind to let me know what is wrong: (1) or (2) .

I will be very thankfull to your help.

Thank you and best wishes


Posted by Rusdy Simano on 28 May, 2008 - 9:27 pm
Referring to IEC60076-1, section 6 paragraph 4:

“Letter symbols for the different windings of a transformer are noted in descending order of
rated voltage. The winding connection letter for any intermediate and low-voltage winding is
immediately followed by its phase displacement ‘clock number’ (see definition 3.10.6).”

Also, definition 3.10.6:

“NOTE The high-voltage winding phasor is taken as reference, and the displacement for any other winding is conventionally expressed by the ‘clock notation’, that is, the hour indicated by the winding phasor when the H.V. winding phasor is at 12 o’clock (rising numbers indicate increasing phase lag)”

So, the right one for a step up transformer, with delta connected primary, and star-connected (with neutral) secondary is:

YNd11

Note: 11 o'clock is the LV winding, which is the primary in a step-up transformer.

Yes, this is confusing, as you wouldn't have a clue just from a transformer vector group, whether it's a step-up or step-down.

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!