Modbus write to register 40002
PCs in Automation topic
advertisement
Posted by Joe Oliphant on 25 April, 2008 - 12:29 am
I'm working with an old ABB ACS400 variable frequency drive. I'm trying to get it to start from a VB program. This requires setting a value to register 40002 and then writing values to the command word at 40001.

I've written similar programs for Allen Bradley and Altivar drives and both of those have odd quirks where you have to write more than one register at a time or write to a goofy offset.

On the above I've used MODBUS/TCP but on this antique, it requires an RS232 and CRC checking.

The ABB drive simply refuses to let me write anything to 40001, 40002, or 40003 but will let me write to any other valid register. Maybe it's something with the CRC. It beats me. I've stumped them at tech support at ABB so if anyone here has any great ideas, I'd appreciate it.

-Joe

Posted by Mark on 25 April, 2008 - 11:45 pm
Hello Joe,

1. Download the MODBUS TCP/IP slave simulator at http://www.peakhmi.com/.

2. Execute your register write to the simulator.

This will validate your code.

If it does not work post your write command stream, in hex, and I will look at it.

Ciao,

Mark
http://www.peakhmi.com/

Posted by Mark on 25 April, 2008 - 11:59 pm
Download Automated Solutions Modbus Master ActiveX Control.

http://automatedsolutions.com/products/modbusrtu.asp

Run the pre-built MiniHMI example application and write to the register that you are having trouble with.

If there is an issue, MiniHMI will provide a detailed error description that should point you in the right direction.

-Mark
www.automatedsolutions.com

Posted by Lee Clore on 26 April, 2008 - 12:19 am
I believe 40002 is mapped to the Control Word Speed (or Torque) reference. You likely can't change it if the Drive is enabled. Depending on the operating macro, you will need to verify the enable or run signal is low before the source can be set. If you are using the DDCS Bus (fiber converter), then forget all that--I think that had more to it...

-Lee

Posted by Lee on 26 April, 2008 - 11:48 pm
Let me clarify that--I think 40002 sets the control word source (ai, comm, keypad, etc.), not the actual reference itself. Something to verify...

Posted by Joe Oliphant on 29 April, 2008 - 1:16 am
I found the problem. You have to be connected through the RS485 port. It will let you change every other register through the RS232 port but not the command word at 40001 or the two holding registers 40002 and 40003.

Anyway, I ordered up a RS232 to RS 485 converter so I'm holding so to say 'till that arrives.

-Joe

Posted by David on 29 April, 2008 - 11:50 pm
Hip Hip Hooray for Joe. He posted some feedback on what he found his problem to be.

His example is worthwhile of emulation.

Thank you, Joe.

David

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!