Member Login
Search
Past & Future Posts
Sponsored Communities
Neat Stuff

Visit our shop for nerds in control lifestyle products.
Cool stuff
Thermal Overload
The threads that wouldn't die...
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
Fortune
The average individual's position in any hierarchy is a lot like pulling
a dogsled -- there's no real change of scenery except for the lead dog.
a dogsled -- there's no real change of scenery except for the lead dog.
RSS Feed
www.control.com/rss
from the khk department...
Moxa and AdamHello,
I want to connect 2 AI and 1 DIO module (ADAM4017p,4055) to Citect SCADA v7 via ethernet. I use rs485/ethernet (Modbus/TCP) convertor (MOXA6110). I can see my modules from Modbus scan software but I can't see them in Citect. My setting is: Modnet protocol, -I192.168.127.2 -P502 -T. The hardware alarm is that device off line. I don't know which setting may be wrong.
With thanks...
I want to connect 2 AI and 1 DIO module (ADAM4017p,4055) to Citect SCADA v7 via ethernet. I use rs485/ethernet (Modbus/TCP) convertor (MOXA6110). I can see my modules from Modbus scan software but I can't see them in Citect. My setting is: Modnet protocol, -I192.168.127.2 -P502 -T. The hardware alarm is that device off line. I don't know which setting may be wrong.
With thanks...
You might consider two things:
First, you might consider obtaining Advantech (they make the Adam modules)
Modbus/TCP converters to replace the Moxa units. This is NOT to suggest
there's anything wrong with the Moxa units-- there probably is not. But then
you have only two people to discuss this with, instead of three.
Second, you should contact Advantech directly-- they have global help
available from www.advantech.com.
Third, you should contact Citect directly-- or through your Schneider
dealer-- whichever provided you the software.
Almost certainly you have a setting or parameter set wrong either in the
Moxa unit or in the Citect setup. Since you can see the Adam modules in a
Modbus scan, my money is on the Citect setup.
If that's the case, calling Citect help directly is probably the fastest way
to get help.
Walt Boyes
Editor in Chief
Control and Controlglobal.com
www.controlglobal.com
Mailto:wboyes@putman.net
Read my blog SoundOFF!! At www.controlglobal.com/soundoff
First, you might consider obtaining Advantech (they make the Adam modules)
Modbus/TCP converters to replace the Moxa units. This is NOT to suggest
there's anything wrong with the Moxa units-- there probably is not. But then
you have only two people to discuss this with, instead of three.
Second, you should contact Advantech directly-- they have global help
available from www.advantech.com.
Third, you should contact Citect directly-- or through your Schneider
dealer-- whichever provided you the software.
Almost certainly you have a setting or parameter set wrong either in the
Moxa unit or in the Citect setup. Since you can see the Adam modules in a
Modbus scan, my money is on the Citect setup.
If that's the case, calling Citect help directly is probably the fastest way
to get help.
Walt Boyes
Editor in Chief
Control and Controlglobal.com
www.controlglobal.com
Mailto:wboyes@putman.net
Read my blog SoundOFF!! At www.controlglobal.com/soundoff
Advantech also has Ethernet versions of their RS-485 devices (6000 series versus 4000 series). The Ethernet version support Modbus/TCP directly. I agree with Mr. Boyes though that this sounds like a Citect problem.
From Control Engineering magazine...
Related articles from Control Engineering magazine- ODVA, DeviceNet: New CIP specs; ControlNet added; 2009 meeting
- Embedded, wireless devices, dynamic IP routing
- Listen in: Wireless developments for Air Force may influence industrial applications
- Easier implementation: Kits for cable testing, wireless products
- Inside look: How MTL Instruments fits with Cooper Industries
- Ethernet hardware: Switches and more
- Frost & Sullivan awards honors many automation, controls companies
- ABB update: User conference, exhibition, flow, SCADA, wireless
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!