Have you tried forcing the logic signal for the suspect alarm on the Mark V (usually it needs to be forced to a logic "1") and observing it on the DCS? Does the DCS display the alarm when it's associated logic signal is forced on the Mark V? I have seen several instances where the wrong signal is placed in the packed register for a particular alarm, and when that alarm is annunciated by the Mark V operator interface it is not annunciated on the DCS because the wrong logic pointname was used in MODBUS.DAT.
Also, how fast is the DCS asking for data via MODBUS? Once per second? Faster? Slower?
If two alarms are annunciated with the same time that means they were detected during the same scan of the CSP. Scan rate should not affect MODBUS information. I have also seen some DCS programmers "multiplex" the MODBUS signals, particularly packed registers, and if the alarm logic was only picked up for one or two scans of the CSP (which is usually one-eighth of a second per scan) the DCS might not detect a change of state occurring that fast. How long did the alarm condition exist? (You should be able to tell us that from the alarm printout information.)
MODBUS won't "broadcast" an alarm the instant it occurs; it's a periodic transfer of information. I believe the MODBUS application on the operator interface polls the Mark V for the data when it gets a request, sends the data to the MODBUS Master, then waits for another request for information before polling the Mark V for the data and sending the data to the Master.
MODBUS is fairly well described in the Mark V Application Manual, GEH-5980, for <I>s. There is a separate manual for GE Mark V HMI implementations of MODBUS, but it's virtually identical from a set-up perspective. More recent GE Mark V HMIs use CIMPLICITY to handle MODBUS communications instead of TCI. Packing is just a more efficient use of registers for transferring data which, usually, doesn't change very often or very fast.
- PTO reports high growth, cross-industry collaboration
- New, efficient industrial gas turbines coming
- Wireless helps Hexion with smoke detection, control room reporting
- Wireless networks for water and wastewater plant: easy, timely info access
- What process control applications are OK for wireless?
- Chemical company processes critical data via wireless Ethernet
- Enclosures: Improve NEMA designs, enclose wireless equipment, keep cabinets cool
- Affiliate integration: Advanced Automation, IAEF and EIAL become Avanceon
- Product experience: Who leads in 2008 with automation system integrators?
- Controller platform: Small-scale system bridges device gap
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Patronize our advertisers!