In our work place we rewinded 2.6KW/7.5KW motor succesfully and tested with tachometer RPM/load current everything same (compare with new motors).
we completed 3Nos of 7.5KW and 5Nos of 2.6KW.
Now we are getting continuous fail. Is there any standard formula related 3 phase Motor rewinding or coil size specification details.
Thanks
Please reply electwar @ gmail.com
Daily i use to update controle.com technical conversation and sharing. Its wonderful!!!!!.
In our work place we rewinded 2.6KW/7.5KW motor succesfully and tested with tachometer RPM/load current everything same (compare with new motors).
we completed 3Nos of 7.5KW and 5Nos of 2.6KW.
Now we are getting continuous fail. Is there any standard formula related 3 phase Motor rewinding or coil size specification details.
Thanks
Please reply electwar @ gmail.com
![]() ![]() |
Hari, it would be fruitless to provide an answer until you furnish some some data:
1) What is failure-rate? Mean-Time-To-Failure?
2) What is the mode-of-failure, i.e., phase-to-earth; phase-to-phase; 3-phase overcurrent; within slot or in terminal box; turn-to-turn; single-phase blowout; pigtails; bearing failure; etc?
3) Are rewind materials, i.e., copper-size, insulation class, the same as original, or upgraded?
4) What about application: one-speed; two-speed; VFD?
5) How about starting method: DOL; conventional reduced-voltage methods; soft-start?
6) You mentioned amperes and speed being the same, but how about: slip; locked-rotor test parameters; uncoupled-test results?
6) Same or different rewinder(s)?
7) What method do you use to remove wire from stator?
8) Are cooling fans (if used) reinstalled?
The above should give you some ideas!
Regards, Phil Corso (cepsicon@aol.com)
1) What is failure-rate? Mean-Time-To-Failure?
2) What is the mode-of-failure, i.e., phase-to-earth; phase-to-phase; 3-phase overcurrent; within slot or in terminal box; turn-to-turn; single-phase blowout; pigtails; bearing failure; etc?
3) Are rewind materials, i.e., copper-size, insulation class, the same as original, or upgraded?
4) What about application: one-speed; two-speed; VFD?
5) How about starting method: DOL; conventional reduced-voltage methods; soft-start?
6) You mentioned amperes and speed being the same, but how about: slip; locked-rotor test parameters; uncoupled-test results?
6) Same or different rewinder(s)?
7) What method do you use to remove wire from stator?
8) Are cooling fans (if used) reinstalled?
The above should give you some ideas!
Regards, Phil Corso (cepsicon@aol.com)
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2013 Nerds in Control, LLC. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.
Fortune
As far as the laws of mathematics refer to reality, they are not
certain, and as far as they are certain, they do not refer to reality.
-- Albert Einstein