Member Login
Search
Past & Future Posts
Sponsored Communities
Neat Stuff

Visit our shop for nerds in control lifestyle products.
Cool stuff
Thermal Overload
The threads that wouldn't die...
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
Fortune
This life is a test. It is only a test. Had this been an actual life, you
would have received further instructions as to what to do and where to go.
would have received further instructions as to what to do and where to go.
RSS Feed
www.control.com/rss
from the control system department...
Modbus communication with Simatic S5 CP521Hello,
We are facing a problem in the communication of Simatic S5 100U CPU-103: 6ES5 103-8MA03 (CP521 Printer interface card: 6ES5 521-8MA11) with ABB 800xA system (CI853-Serial communication card).
Simatic S5 system is presently communicating with Yokogawa Microexcel's DCS RS2 (Suffix C) card. We don't know exactly about the communication protocol used with Yokogawa Microexcel system. Our requirement is to establish communication of Simatic system with ABB 800xA system via Modbus.
Does CP521 card support Modbus communication?
If not, is there any mode of communication available?
We need help from your side for this issue.
We are facing a problem in the communication of Simatic S5 100U CPU-103: 6ES5 103-8MA03 (CP521 Printer interface card: 6ES5 521-8MA11) with ABB 800xA system (CI853-Serial communication card).
Simatic S5 system is presently communicating with Yokogawa Microexcel's DCS RS2 (Suffix C) card. We don't know exactly about the communication protocol used with Yokogawa Microexcel system. Our requirement is to establish communication of Simatic system with ABB 800xA system via Modbus.
Does CP521 card support Modbus communication?
If not, is there any mode of communication available?
We need help from your side for this issue.
There is a special memory module that you can get to plug into most models of CP521. This memory module has firmware with the Modbus RTU protocol programmed into it. I think you also need some special function blocks in the PLC CPU so the CPU will talk to the CP521 (I think these come on a disk). However, there are several different models and versions of CP521. I don't know if this works with the one you have. You'll have to look that up for yourself on the Siemens web site.
If your CP521 has a memory module plugged into it, it may have Modbus RTU already. You would need to read the part number off the memory module and look it up on the Siemens web site. A memory module (if present) is an optional part, so it has a separate part number from the CP521 itself.
If you already have Modbus, then you need to make sure things like baud rate, parity, etc. are all set correctly. I would suggest looking up more information on the Yokogawa system so you can find out what it is already doing.
If your CP521 has a memory module plugged into it, it may have Modbus RTU already. You would need to read the part number off the memory module and look it up on the Siemens web site. A memory module (if present) is an optional part, so it has a separate part number from the CP521 itself.
If you already have Modbus, then you need to make sure things like baud rate, parity, etc. are all set correctly. I would suggest looking up more information on the Yokogawa system so you can find out what it is already doing.
Hi there,
One way of solving the problem could be to use a gateway. I assume that your Simatic S5 acts as Profibus master and that the ABB 800xA acts as Modbus master. In such a case, a gateway that is a Profibus slave and Modbus slave would be work.
For more info of the gateway, go to:
http://www.anybus.com/support/support.asp?PID=185&ProdType=Any bus%20X-gateway
or email me at: support@hms.se
/Pat
One way of solving the problem could be to use a gateway. I assume that your Simatic S5 acts as Profibus master and that the ABB 800xA acts as Modbus master. In such a case, a gateway that is a Profibus slave and Modbus slave would be work.
For more info of the gateway, go to:
http://www.anybus.com/support/support.asp?PID=185&ProdType=Any bus%20X-gateway
or email me at: support@hms.se
/Pat
From Control Engineering magazine...
Related articles from Control Engineering magazine- ODVA, DeviceNet: New CIP specs; ControlNet added; 2009 meeting
- Embedded, wireless devices, dynamic IP routing
- Listen in: Wireless developments for Air Force may influence industrial applications
- Easier implementation: Kits for cable testing, wireless products
- Inside look: How MTL Instruments fits with Cooper Industries
- Ethernet hardware: Switches and more
- Frost & Sullivan awards honors many automation, controls companies
- ABB update: User conference, exhibition, flow, SCADA, wireless
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.
Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!