XBT GT4330 problem communications
Communications systems and equipment. topic
Posted by Lapic on 15 July, 2008 - 12:13 am
Problem with communications between Twido PLC and Magelis (XBT GT 4330). Message on touch screen is: "No replay from PLC". I use a XBTZ978 cable. Is it a problem with the cable or with the address? Please help me!!


Posted by 4k05 on 16 July, 2008 - 2:07 am
http://www.control.com/thread/1026230486#1026247374

Check this, it should help. It describes cables.

Make sure you have the communication parameters set correctly and that the settings are the same on the HMI and on the PLC (Baud, parity, stop bit...). Check also that the Modbus master protocol is selected on the panel.

If nothing works, update your firmware on your panel, make sure you use the newest version of the panel programming software.


Posted by Aggattapauer on 17 July, 2008 - 2:15 am
You need the new cable XBT9780, or you may use the XBT978 with an adapter XBTZ999.

It is easier to change the pin-out of your XBT978.


Posted by Dweebyone on 17 July, 2008 - 2:18 am
Cable should be XBTZ9780, the XBTZ978 has channels A & B reversed. This is an obsolete old cable.

Make sure Vijeo designer application is pointing to com2, not com1 default port.

Parity should be none, in Twido and Vijeo application, obviously baud rate, stop bits, etc. must be the same on both devices.

Make sure that registers you are using in the Vijeo Designer application are actually reserved, or used in Twido application.

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!