%impedence of power transformer
Engineering topic
advertisement
Posted by ramesh on 5 August, 2008 - 1:12 am
Please elaborate on % impedence of power transformer.

Posted by Ananymous on 6 August, 2008 - 11:28 pm
"The percentage impedance of a transformer is the volt drop on full load due to the winding resistance and leakage reactance expressed as a percentage of the rated voltage."

"It is also the percentage of the normal terminal voltage at on side required to circulate full-load current under short circuit conditions on other side."

The impedance of a transformer has a major effect on system fault levels. It determines the maximum value of current that will flow under fault conditions.

It is easy to calculate the maximum current that a transformer can deliver under symmetrical fault conditions. By way of example, consider a 2 MVA transformer with an impedance of 5%. The maximum fault level available on the secondary side is:

2 MVA x 100/5 = 40 MVA

and from this figure the equivalent primary and secondary fault currents can be calculated.

A transformer with a lower impedance will lead to a higher fault level (and vice versa).

The figure calculated above is a maximum. In practice, the actual fault level will be reduced by the source impedance, the impedance of cables and overhead lines between the transformer and the fault, and the fault impedance itself.

Posted by Phil Corso on 7 August, 2008 - 12:45 am
Responding to Ramesh’s 5-Aug-08 (00:12) request... following is a simplified discussion:

A transformer’s impedance (also referred to as impedance-voltage) is equal to the voltage, in % of its rated-voltage, that when applied to the primary-winding of a transformer will cause rated-current to flow in its shorted secondary-winding. For example, consider a transformer rated 500kVA, 6kV/400V, and 4.0% impedance. It means that when 240V is applied to the primary-winding, then the rated current, 720A, will flow in the shorted secondary.

To elaborate, consider a two-winding transformer having an equal number of turns in its primary and secondary windings. The effective transformer resistance is the sum of the primary and secondary resistances. Similarly, the effective transformer reactance is the sum of the primary and secondary leakage reactances. Finally, the effective transformer impedance is the vector addition of its effective resistance and reactance.

If additional information is required, let me know!

Regards, Phil Corso (cepsicon@aol.com)

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2008 Reed Business Information. Subject to its Terms of Use.

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2008 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, PostgreSQL and Apache. Be happy.

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!