Member Login
member
passwd
remember me on
this computer.

- join now -
- forgot username or password? -

Search

Jump to a Date

Sponsored Communities
Cool stuff
Select a topic of interest:
...and press:
Neat Stuff
Control.com Stuff

Visit our shop for nerds in control lifestyle products.

Fortune
Mencken and Nathan's Fifteenth Law of The Average American:
The worst actress in the company is always the manager's wife.
RSS Feed
RSS feed Use this link to get an RSS feed of the Control.com article flow, for private, non-commercial use only:
www.control.com/rss/
To get a personalized feed, become a member at no cost.
Select a Page Style
Select one of the following styles:
- BluFu
- Classic
(cookies required)
advertisement
from the Automation List department...
suggest a control scheme for regulating three control valves in Auto
Continuous process industries, DCS questions. topic
Posted by abhi on 16 August, 2008 - 1:08 pm
Problem: We are not able to run the Furnace in Temperature Auto mode(1200 deg C) & we do not know the control philosophy

There are three control valves:
For Air with Flow meters ( 4-20 Ma O/p)
For BF with Flow meters ( 4-20 Ma O/p)
For Propane with Flow meters ( 4-20 Ma O/p)
Two S type T/c are there ( Range 0 to 1400 deg C) (4-20 ma)

The Mixed Gas ( BF & Propane ratio is:
Bf Gas : 94% ,calforic value: 700K cal/m3( 2930 kj/m3)
Propane gas: 6 % ,,calforic value: 22690 k cal/m3

As Blast Furnace gas ( BF Gas) is free & Propane is very costly , intially For statring of furnace Propane is used but when temp is about 700 deg ,less propane & more BF gas is used
Can you help in suggesting a control scheme for regulating three control valves in Auto.


Posted by Rob on 5 September, 2008 - 1:37 am
Well, it sounds like you have two operating modes:

1. Startup when < 700 degrees is a regular PID control of temperature using the Propane Valve Only. The Air flow PID setpoint is calculated to give the correct Propane/Air ratio, based on measured propane flow.

2. Operation when > 700 degrees. At this point you want to Maximise Bf Gas. To do this set up the temperature PID control as a split range controller. For a temperature PID output of 0-50%, the BF gas valve is controlled 0-100%. When the output of the temperature control is 50 - 100%, Bf Gas flow is maxed out and Propane gas valve is controlled 0 - 100%. Again, calculate the Air flow setpoint based on the measured flows of Bf & Propane.

There are some complications you will need to deal with ....

1. The tuning of the temperature control will probably vary depending on whether you are using Bf or Propane. You should be able to solving this by using 2 sets of Adaptive tuning values

2. You probably can't just swap from startup mode to operating mode without causing a bump in the temperature. You might need to have some sort of transition logic to ramp down the propane valve & ramp up the Bf gas valve.

You could also use a Cascade arrangement with temperature as the Master PID loop and Bf & Propane Flows as slave PID loops, but I don't think there is any point to this as it complicates the control for little advantage.

My 2c

www[.]lymac.co.nz


Posted by Ron Wensley on 5 September, 2008 - 9:51 pm
Another part of the control scheme that is often overlooked when you are transferring from one control source to another is de-coupling.

Your two source of fuel, BF gas and propane have different heating values, pressures, valve types/characteristics, physical line differences, transport times, and time constants.

While it is common to simply have a PID controller for each valve these two controllers need to be decoupled. As the propane valve moves the BF valve needs to be aware of the movement for the process responds. Like wise when the propane valve moves the BF valve needs to be aware of it before the process responds.

By carefully setting up a decoupling network you can greatly improve the robustness and controllability of your system.

From Control Engineering magazine...
Related articles from Control Engineering magazine
Above articles copyright 2009 Reed Business Information. Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2009 Control Technology Corporation. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.

Internet Explorer 6.0 Fix

Advertisement
Our Advertisers
Help keep our servers running...
Patronize our advertisers!