Member Login
Search
Jump to a Date
Sponsored Communities
Cool stuff
Neat Stuff

Visit our shop for nerds in control lifestyle products.
Thermal Overload
The threads that wouldn't die...
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
- PC reliability?
- Windows, real time
- PID loops
- PCs vs. PLCs
- Replacing people
- MS 'monopoly'?
- Software quality
- Where do we go from here?
- Why pay?
Fortune
Goldenstern's Rules:
(1) Always hire a rich attorney
(2) Never buy from a rich salesman.
(1) Always hire a rich attorney
(2) Never buy from a rich salesman.
RSS Feed
www.control.com/rss/
To get a personalized feed, become a member at no cost.
We have a Gas turbine
TG-702 S.No. : 281817 with Speedtronic control mark-5, with DOS based I.
Following Alram appeared on the alarm display.
16-AUF-2008 08:14:15.000 T2 1* Q 0000 DIAGNOSTIC ALARM <C> <Q>
In the Diagnostic Alarm display following alarms were present.
16-AUG-2008 08:14:14.000 T2 0* R 0009 DCC DPM:INVALID DESTINATION ADDRESS
16-AUG-2008 08:14:14.000 T2 0* R 0005 DCC NO queue server for distination
16-AUG-2008 08:14:09.000 T2 0* C 0009 DCC DPM:INVALID DESTINATION ADDRESS
16-AUG-2008 08:14:09.000 T2 0* C 0005 DCC NO queue server for distination
When these alarms were ACKed and Reset they disappeared.
What might be the reason behind these alarms.
What steps can be taken to stop recurrence of these alarms.
Can these alarms cause the Gas Turbine to Shutdown.
TG-702 S.No. : 281817 with Speedtronic control mark-5, with DOS based I.
Following Alram appeared on the alarm display.
16-AUF-2008 08:14:15.000 T2 1* Q 0000 DIAGNOSTIC ALARM <C> <Q>
In the Diagnostic Alarm display following alarms were present.
16-AUG-2008 08:14:14.000 T2 0* R 0009 DCC DPM:INVALID DESTINATION ADDRESS
16-AUG-2008 08:14:14.000 T2 0* R 0005 DCC NO queue server for distination
16-AUG-2008 08:14:09.000 T2 0* C 0009 DCC DPM:INVALID DESTINATION ADDRESS
16-AUG-2008 08:14:09.000 T2 0* C 0005 DCC NO queue server for distination
When these alarms were ACKed and Reset they disappeared.
What might be the reason behind these alarms.
What steps can be taken to stop recurrence of these alarms.
Can these alarms cause the Gas Turbine to Shutdown.
First of all it might be helpful to understand the acronyms in the alarm text messages.
DCC (Drive Control Card) - The main card with the microprocessor, RAM, & EEPROM chips on it DPM (Dual-Ported Memory) - An area of RAM where signal values are placed and can be accessed by other processors
So, it would seem that something is asking for either a signal value for which there is no signal, or the signal type being requested is not valid. Another, less likely, possibility would be that there is a problem with the dual-ported memory. DCC cards were the first cards used in the early production of Mark Vs. It could be the card components are getting "old" and have been exposed to excessive heat and/or humidity. But I would expect lots of these alarms which couldn't be acknowledged and reset.
How long have these alarms persisted? If they just started recently, was it after someone was making some kind of changes to the <I>, possibly running the Total Job Compiler (MK5MAKE), or making changes to a MODBUS.DAT file? Or to some the DCS or other system which might be communicating with the Mark V through the <I> via MODBUS? Was the processor recently re-booted or was it downloaded to, and the same information was not downloaded to the other processors, or vice versa, nothing was downloaded to this processor but only to the other processors?
Unless these alarms increase in quantity and frequency and cannot be reset, they should not cause a turbine shutdown/forced outage.
DCC (Drive Control Card) - The main card with the microprocessor, RAM, & EEPROM chips on it DPM (Dual-Ported Memory) - An area of RAM where signal values are placed and can be accessed by other processors
So, it would seem that something is asking for either a signal value for which there is no signal, or the signal type being requested is not valid. Another, less likely, possibility would be that there is a problem with the dual-ported memory. DCC cards were the first cards used in the early production of Mark Vs. It could be the card components are getting "old" and have been exposed to excessive heat and/or humidity. But I would expect lots of these alarms which couldn't be acknowledged and reset.
How long have these alarms persisted? If they just started recently, was it after someone was making some kind of changes to the <I>, possibly running the Total Job Compiler (MK5MAKE), or making changes to a MODBUS.DAT file? Or to some the DCS or other system which might be communicating with the Mark V through the <I> via MODBUS? Was the processor recently re-booted or was it downloaded to, and the same information was not downloaded to the other processors, or vice versa, nothing was downloaded to this processor but only to the other processors?
Unless these alarms increase in quantity and frequency and cannot be reset, they should not cause a turbine shutdown/forced outage.
No compilation or reboot was in progress.
Nothing was downloaded to any processor.
Just before the alarm the Monitor of Local <I> was turned OFF and then again ON. Only the monitor not the I processor.
These alarms did not persist for long, and their state changed from 1 to 0 automatically.
After being Acked and reset they have not appeared again so far.
Nothing was downloaded to any processor.
Just before the alarm the Monitor of Local <I> was turned OFF and then again ON. Only the monitor not the I processor.
These alarms did not persist for long, and their state changed from 1 to 0 automatically.
After being Acked and reset they have not appeared again so far.
From Control Engineering magazine...
Related articles from Control
Engineering magazine- Budget-friendly temperature control unit
- Upgrading control for better polymer performance
- Software pinpoints process interactions
- BP selects SIS for UK deployment
- Here's what you need to know about controls, says Automation Federation, U.S. government
- Electrical product safety: Are testing labs needed or is a supplier's declaration enough?
- Automation vendors boost biofuels
- Cyber security issues take center stage in 2009
- AIC Series presents new high energy storage chokes
- Decrease arc flash risk with new motor control center option
Above articles copyright 2009 Reed Business Information.
Subject to its Terms of Use.
Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2009 Control Technology Corporation. All rights reserved.
Our Advertisers
Help keep our servers running...
Patronize our advertisers!
Patronize our advertisers!